On the pump body, will send photo.Where is the arrow?
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Discuss Any ideas? Unreliable heating. in the Central Heating Forum area at Plumbers Forums
On the pump body, will send photo.Where is the arrow?
The picture of the old pump (blue) is rotated. The writing on it was upside down. It was the pump installed when the house was built.What do you mean by upside down? the pump label etc may be upside down but all that matters is that the arrow on the pump body is pointing in the correct direction.
Your picture is only darkness.
Yes, it is pointing downward
So, are you absolutely certain that the new pump is pumping in the same direction as the old one, ie, the arrow on the old pump was also pointing downwards??, Is you system as I showed above or can you post a photo of it?, its strange that you are getting problems at CP2 even though it is a bit high so CP1 may sort out the problem, was that system chemically cleaned or anything like that between pump changes?.
Yes, that's where the 3 port valve isWell you will have to be happy (ensured) that the UPS3 is pumping in the correct direction before taking any drastic or unnecessary action, if the pipe coming out of the bottom of the pump then goes to either a three way valve or to a number of valves (all/any of which will have a motor with a cable) then pump direction is downwards, if these valve(s) come off the top pipe then the pump must pump upwards.
The pump was making a very strange noise. The file I added was a video file.so 3 port below pump and pump pumping downwards is correct, CP1 or just maybe PP2 next step??
WhT was happening when the pump was stopping as can't see it
The arrow is downwards on the left side behind the cable socket. I can't see anything on the right hand side. Best photo I can take given the angle is here.Gary, getting a bit confused myself re arrow on pump, can you just confirm that (if) the pump is now pumping downwards then the engineer will then have turned the head through 180 deg and the arrow will be on the right hand side of the pump body, pointing downwards.
Assuming it was how is your system performing now?.
Got closer. Yes arrow on right is downwards.Not getting anywhere really. I had to leave heating on today as someone was home so it was on CP1 with all upstairs rads off so the living room rads were warm. The kitchen rads beyond those never really warmed up properly. Have tried to restart CP1 following the process I was asked to go through on Sunday evening but when I switch upstairs rads off there heat is not too hot downstairs with the last 2 or 3 on system almost getting nothing. Like i say I am not a plumber so have no knowledge at all but I know when it won't work just by noise of pump. When it is almost silent I know it will work but when it makes more noise it won't. I think I need to have the system cold to be able to try a proper CP1 or PP1 reset.
All inlet valves downstairs are scorching hot. All rads have been bled. First 3 rads on system downstairs are warm but there 4 after that are not.Got closer. Yes arrow on right is downwards. View attachment 80051
What does venting air mean?Very strange allright, presume not something daft like the pump valves not opened fully, they look like gate valves so should be ~ 3 or 4 full turns from fully shut to fully open. There arn't too many things left, the pump was probably changed out without drain or partial system drain down, possible sludge build up but unlikely except the F&E tank was full of crap and drained down into the system. (if system drained)
The possibility of a faulty UPS3 still exists but if so unlikely that air would continue to build up, are you still venting air, you say all rads have been bled?.
CP1 at 3M should not cause any problems and is required for most systems of your size, my system runs at 3.5/3.6M with the (Wilo) pump set to a PP setting of 4.6M.
John, should the gate valve directly under the pump be fully open? The middle of the three you can see in the photo I uploaded yesterday.What does venting air mean?
Opening the vent screws and getting rid of any air in the rads. (Bleeding the rads)What does venting air mean?
Not sure about the one with the red handwheel (you would have to trace it but let it be just now whatever its opening is).John, should the gate valve directly under the pump be fully open? The middle of the three you can see in the photo I uploaded yesterday.
Cheers. In work now so will try again when I get home late afternoon.Opening the vent screws and getting rid of any air in the rads. (Bleeding the rads)
Not sure about the one with the red handwheel (you would have to trace it but let it be just now whatever its opening is).
The two brass valves, immediately above and below the pump MUST be fully open, get a adjustable spanner or even a pliers and try shutting first, if they are open then you should get 3 to 4 turns to shut, then immediately reopen, ie they must be ~ 3 to 4 full turns open from fully shut.
That middle pipe seems to go into the bottom of the immersion heater.Cheers. In work now so will try again when I get home late afternoon.
Yes, all rads are bled - doing it all the time. No air in them.Opening the vent screws and getting rid of any air in the rads. (Bleeding the rads)
Not sure about the one with the red handwheel (you would have to trace it but let it be just now whatever its opening is).
The two brass valves, immediately above and below the pump MUST be fully open, get a adjustable spanner or even a pliers and try shutting first, if they are open then you should get 3 to 4 turns to shut, then immediately reopen, ie they must be ~ 3 to 4 full turns open from fully shut.
probably the cold water supply to your HW cylinder.That middle pipe seems to go into the bottom of the immersion heater.
Thanks John. I have bled the rads but not emptied them per se - when you say 'no circulation or corc pump defective' what else could cause the 'no circulation'? The weird thing is that on Sunday after I changed to CP2 all rads were hot, same Monday but then Monday night the downstairs rads went cold. So that must be an airlock? But there is no air in rads! Given that we have had heat i would guess the pump valves are fully open.If no air in them then pointless venting, except that you are getting some heat in them by actually bleeding off a few litres of water which means no circulation or circ pump defective, CP2 at 4.5M even with all rads open (no balancing) should circulate plenty of water to get all/most quite hot, you have another problem IMO.
When you come home and if you find that the pump valves are fully open (and probably are) then may have to check the circ pump.
probably the cold water supply to your HW cylinder.