Does anyone have any recommendations or suggestions for a sleeve for the earth cable so it can be put safely through the cavity wall near to the gas meter box?
Assuming it's outside the box, and it's going straight across the cavity, I'd be interested to know whether electrical regulations strictly require a sleeve? If not, then I'd suggest any common sense material (offcut of pipe or hose) would do as they would class as a cable installation aid.
Assuming it's outside the box, and it's going straight across the cavity, I'd be interested to know whether electrical regulations strictly require a sleeve? If not, then I'd suggest any common sense material (offcut of pipe or hose) would do as they would class as a cable installation aid.
right thanks, just with it being probably near the meter installation thought it would be for the best. cemented in place and with a good bit of non setting compound perhaps in the end. they suggested 20mm conduit on the electrician forum
Today the company have replied to a recent initial email I sent with the photos saying:
"Hi,I have returned from annual leave this morning , I will investigate this and get back to you when I have more information. Are you happy for us to seal the wire? Thank you"
I havent replied with an alternative yet. Just wanted to formulate the best counter suggestion.
Yep also it’s modifying the meter box technically as it’s not an approved hole so needs a new meter box and the earth moving externally or via an approved entry
I found this thread on the Electricians forum, I was not aware us sparks could not drill a hole in the meter box, but now I know, it makes sense. Maybe I'm the only spark that does not know this, but I doubt it. There is nothing in our regs, and we are the ones fitting the bonding, so the IET should include this in our regs so we don't continue to do this. But as commented previously, there must be loads of boxes that do not comply. Replacing the whole box seems over the top if this is the only non compliance.
Looking at the regs snip, it seems to me that the requirement is to make the rear part of the box air tight. I'm thinking a Wylex Membrane Cable Entry gland should be sufficient. I know the Wiska membrane glands are IP66, I assume Wylex will be the same. So this could be an easy fix ?
The muppets come up with electrical changes to justify new books, exams etc and they can’t even check they are understandable or logical. And they rarely correct earlier mistakes or errors.
With the 18th edition, the printed version was slightly different to the electronic version😁
The only opening in a built in gas meter box should be the outlet pipework spigot which must be fitted with the spigot adaptor to form a conduit through the cavity. Earthing should preferably be attached to the gas pipe immediately inside the property and the spigot sealed with non setting compound. No other holes are permitted in the box. The reason why of course is that such holes would permit gas leakage from within the box to enter the wall cavity.