Hoping that someone might be able to help me.

I have a sealed heating system comprising 15 radiators and hot water cylinder. In the last 18 months all radiators were replaced and plumbed using 10mm microbore pipe back to manifolds on 22mm flow and return pipes. The system is S plan with two heating zones and hot water.

The problem I am having is that the auto bypass lets hot water through in any combination. When both upstairs and downstairs heating is on the boiler stays on and good heat is achieved, although bypassing. When upstairs is on in isolation the bypass is open and the boiler starts short cycling and also does the same with hot water only.

Initially I was concerned that the microbore pipe was causing too much resistance of flow which was resulting in the auto bypass opening. However, the bypass also opens for hot water only which is not in small bore pipe so makes me think it is not this.

I have had the auto bypass replaced, so it is not a faulty valve.

The pump was re-used from the old system and is a 15/50, I wonder if this is not man enough to overcome the resistance of the new small diameter pipes? But this would not explain the bypass being open for hot water only?

My other line of thinking is that the heat exchanger may be clogged up causing a restriction, we are in a hard water area and had a period where the boiler was kettling last year.

Overall the heating and hot water work, but not as well or efficiently as I believe they could. Really I'd like to find a heating engineer in Norfolk who really knows their stuff, a couple of people local to me have been round and I've been advised to change the boiler which I just don't believe.
 
Hoping that someone might be able to help me.

I have a sealed heating system comprising 15 radiators and hot water cylinder. In the last 18 months all radiators were replaced and plumbed using 10mm microbore pipe back to manifolds on 22mm flow and return pipes. The system is S plan with two heating zones and hot water.

The problem I am having is that the auto bypass lets hot water through in any combination. When both upstairs and downstairs heating is on the boiler stays on and good heat is achieved, although bypassing. When upstairs is on in isolation the bypass is open and the boiler starts short cycling and also does the same with hot water only.

Initially I was concerned that the microbore pipe was causing too much resistance of flow which was resulting in the auto bypass opening. However, the bypass also opens for hot water only which is not in small bore pipe so makes me think it is not this.

I have had the auto bypass replaced, so it is not a faulty valve.

The pump was re-used from the old system and is a 15/50, I wonder if this is not man enough to overcome the resistance of the new small diameter pipes? But this would not explain the bypass being open for hot water only?

My other line of thinking is that the heat exchanger may be clogged up causing a restriction, we are in a hard water area and had a period where the boiler was kettling last year.

Overall the heating and hot water work, but not as well or efficiently as I believe they could. Really I'd like to find a heating engineer in Norfolk who really knows their stuff, a couple of people local to me have been round and I've been advised to change the boiler which I just don't believe.
Can you produce a drawing please then we can all have a go,at this just attach it
Rob Foster aka centralheatking
 
Hi Chris, can you set this bypass valve or do they come pre set? I have had a look online and some people have had to adjust theirs. I could understand if it opened for the mass amount of micro bore but the hot water is puzzling.

I am not a plumber just a student at the minute so I don’t want to offer any advice but I am interested in your problem. Best of luck.
Ben
 
Pump is wrong type.
But you also need your bypass valve adjusted to only open when system is operating with one radiator on, or when pump overrun is on.
Your heating installer should have done all that
 
If my memory serves me correctly, the bypass should be set up for the index circuit ( furthest radiator or the circuit with most resistance) this would have to be calculated to find the flow rate to set the bypass.
 
Ok thanks, I contacted Grundfos and they recommended even going to a 8m pump.

One thing I don't understand is the pumps marked 15 50/60 that are ok for 5m or 6m systems. Surely it can't be both?

A hot water cylinder and then 15 radiators on 2 zones supplied from
10mm coming from 22mm and Grundfos recommend 8m pump?
What is the total kw needed?

A 6m pump will do approx 35 kw.
Normally no bother on 10mm pipes if they are piped correctly and runs are not long.

The fact that you have 22mm pipes suggests your heat requirements are fairly modest.

I would guess you only need a 6m pump and also make sure the bypass is not bypassing when most of the system is supposed to be open flow.

Your installer has clearly not fitted correct pump and should have warned you
 
A hot water cylinder and then 15 radiators on 2 zones supplied from
10mm coming from 22mm and Grundfos recommend 8m pump?
What is the total kw needed?

A 6m pump will do approx 35 kw.
Normally no bother on 10mm pipes if they are piped correctly and runs are not long.

The fact that you have 22mm pipes suggests your heat requirements are fairly modest.

I would guess you only need a 6m pump and also make sure the bypass is not bypassing when most of the system is supposed to be open flow.

Your installer has clearly not fitted correct pump and should have warned you

I'll get back to you on the KW but it is less than 35.

All the manifolds are located in the upstairs hallway so a lot of the 10mm runs for downstairs go across a room and then down and back again. The longest run is probably 8 or 9 m each way. But most are around 5m downstairs. Interestingly the downstairs radiators heat up better than upstairs.

Grundfos said the pump I mentioned is their recommendation for an average 4 bed!

So could an under sized pump cause the bypass to open?

I have a heating engineer coming next week but would be good to point him in the right direction.
 
Here you go, this is all located about 2m from the boiler.

IMG_20181101_080844.jpg
 
Will get some more photos for you later. I've (perhaps stupidly) adjusted the bypass valve and it still passes on the highest setting.

It would definitely appear that my pump is undersized, if it cannot overcome the frictional head of the pipework could this cause the bypass to open?

Some more details for you all.

  • Pipework from boiler is 28mm reducing to 22mm at zone valves.
  • Boiler is a British Gas 330 which I believe has a maximum output of 31kw.
  • Downstairs radiators total 28560 BTU which I think is 8.4 kWh?
  • Upstairs radiators total 17445 BTU which I think is 5.1 kWh?
  • Zone valves, expansion tank etc is located in the garage at about the same level as the first floor.
  • Manifolds are located within the first floor hallway. So downstairs radiators have greatest runs of 10mm, up to 9m each way, probably averaging about 5m each way.
  • Upstairs has shorter runs, probably ranging from 1m to 4m each way.
  • Downstairs radiators seem to heat up quite nicely despite the longer runs.
  • Upstairs radiators don't heat up particularly well due to boiler cycling if upstairs zone is on only. Also radiators with short runs have to be throttled right back to get heat to the radiators with longer runs.
 
Are you turning the bypass towards closed position in clockwise direction?

A minor point, but the head of the pump should have been turned 180 degrees to keep the electrics on top. Your installer probably didn’t do that because he didn’t want to disturb the seal in a second hand pump, to be fair to him.
 
Are you turning the bypass towards closed position in clockwise direction?

A minor point, but the head of the pump should have been turned 180 degrees to keep the electrics on top. Your installer probably didn’t do that because he didn’t want to disturb the seal in a second hand pump, to be fair to him.

Yes clockwise.

I was starting to think that an upgraded pump might solve my problem but that wouldn't explain why its bypassing on hot water only? I would have thought this circuit has a very low resistance?
 
I can't help wondering if the system has been balanced for the correct temperature differential.

The British Gas 330 boiler has a maximum output of 30kW but is set, at the factory, to give 18kW. As there are only 13.5kW of rads, I would assume the output has not been changed. The boiler is designed to have a flow-return differential of about 20°C. With a 20°C drop the head loss through the boiler, at 18kW, is about 0.9m. This would leave about 3m available from the 15-50 on speed 3 for the head loss in the radiator circuit.

If the system has been balanced for a differential of about 10°C, the flow rate will double and the boiler head loss alone will be about 3.6m (four times greater), which is more than a 15-50 can deliver. This would not someone trying to balance for an 10°C, even if they could only achieve something higher.
 
I can't help wondering if the system has been balanced for the correct temperature differential.

The British Gas 330 boiler has a maximum output of 30kW but is set, at the factory, to give 18kW. As there are only 13.5kW of rads, I would assume the output has not been changed. The boiler is designed to have a flow-return differential of about 20°C. With a 20°C drop the head loss through the boiler, at 18kW, is about 0.9m. This would leave about 3m available from the 15-50 on speed 3 for the head loss in the radiator circuit.

If the system has been balanced for a differential of about 10°C, the flow rate will double and the boiler head loss alone will be about 3.6m (four times greater), which is more than a 15-50 can deliver. This would not someone trying to balance for an 10°C, even if they could only achieve something higher.

Thanks, I don't really know what you mean by your last paragraph? What differential should be looked for at the radiators to achieve 20C at the boiler?

I know that the system was not balanced following the change of radiators / pipework. From everyone's input I'm thinking I should ask for the following to be investigated.

1. Change pump to a higher rated one, probably 6m.
2. Check that boiler output has not been adjusted from 18kw, if it has get it changed back.
3. Carry out full balance of system.
4. Re-set bypass valve, change if required.
 
Thanks, I don't really know what you mean by your last paragraph? What differential should be looked for at the radiators to achieve 20C at the boiler?
I'm sorry for confusing you. The last sentence should read:

"This would not stop someone trying to balance for an 10°C, even if they could only achieve something higher."

In the past, before condensing boilers, the standard was to balance the system - that's boiler and rads - for an 11°C (actually 20°F, which shows how old it is) differential. This has changed to 20°C for two reasons: to reduce the head loss due to friction, particularly due to the heat exchanger which tend to have very narrow pathways; and so the return temperature is closer to the dew-point of natural gas (55°C), which is the temperature at which condensing begins (It increases as return temperature drops.).

A condensing boiler should be balanced for a drop, across boiler and rads, as close to 20°C as possible, but not any higher. You may not be able to achieve 20°C due to the way the pump interacts with the system.

You may find that balancing the system will remove the need to replace the pump. There is over 3m of head available for the index circuit.
 
Last edited:
I based the info above on the boiler's output of 18kW. You have only 13.5kW of rads so the boiler will modulate to that output. This means a flow rate of 580 litre/hr giving a heat exchanger head of 0.5m and an available pump head of 3.5m at speed 3. This should be more than enough.
 

Similar plumbing topics

  • Question
With the system as it is at the moment, I'd...
Replies
6
Views
2K
I should have said "S-plan plus", of course!