Thanks, makes sense to me. Although is 3.5m head sufficient for the longest microbore to manifold circuit of 18m? My rough calculations would suggest not.

And it seems like that was too long in the first place but that's a different story.
 
Too late for me to read all this. Basically, a pump that is too weak for the job will NOT be opeing the bypass. My experience with differential pressure auto bypasses is that they can very easily be jammed very slightly open with a bit of crud from the system and then they let by, even when the head is not sufficient to overcome the spring pressure.

If, as I suspect, your system is old and has a lining of black stuff on the pipe bores, I wonder if a bit of this could have got in between the valve seat and seal on your ABV when it was last forced to open and this has lodged there. I once tried an experiment in my own house with an ABV going through a bypass radiator, but, after the valve got jammed slightly open a second time in the same number of weeks, I gave it up.
 
I know that the system was not balanced following the change of radiators / pipework. From everyone's input I'm thinking I should ask for the following to be investigated.

1. Change pump to a higher rated one, probably 6m.
2. Check that boiler output has not been adjusted from 18kw, if it has get it changed back.
3. Carry out full balance of system.
4. Re-set bypass valve, change if required.
Changing the pump to a 6m head one will only make the by-pass opening worse however you my need a higher head pump to over come the resistants of the micro bore system, so what is to be done.

First thing to understand is why we need a by-pass in the first place.
The main reason (& in this case) is to maintain a minimum flow rate through the boiler at all times, this allows the boiler controls to adjust the burn of fuel to try to achieve a 20deg C difference between the flow & returning water. The system is pressure dynamic, that is to say zone & TRV valves are opening & closing all the time so the work the pump has to do keeps changing. With all the valves open the pump needs move a lot of water (heat) but with only enough force to overcome the resistance in the whole circuit. As the valves close the flow rate around the circuits will decrease but the pressure generated by the pump will rise (they are directly related, see pump graphs).
You have fixed speed pump installed so the pressure will climb, this rise in pressure was used to open a auto by-pass valve at the point were the minimum flow rate required by the boiler manufacturers was not going to be achieved. This sudden opening between the flow & return should send hot water straight back to the boiler raising the return temperature which would cause the boiler to turn off on the boiler stat.
What are the options then?
 
Changing the pump to a 6m head one will only make the by-pass opening worse however you my need a higher head pump to over come the resistants of the micro bore system, so what is to be done.

First thing to understand is why we need a by-pass in the first place.
The main reason (& in this case) is to maintain a minimum flow rate through the boiler at all times, this allows the boiler controls to adjust the burn of fuel to try to achieve a 20deg C difference between the flow & returning water. The system is pressure dynamic, that is to say zone & TRV valves are opening & closing all the time so the work the pump has to do keeps changing. With all the valves open the pump needs move a lot of water (heat) but with only enough force to overcome the resistance in the whole circuit. As the valves close the flow rate around the circuits will decrease but the pressure generated by the pump will rise (they are directly related, see pump graphs).
You have fixed speed pump installed so the pressure will climb, this rise in pressure was used to open a auto by-pass valve at the point were the minimum flow rate required by the boiler manufacturers was not going to be achieved. This sudden opening between the flow & return should send hot water straight back to the boiler raising the return temperature which would cause the boiler to turn off on the boiler stat.
What are the options then?

Fit a Grundfos pump with proportional pressure function? God knows, that's why I'm asking! Someone else must have come across this before?
 
If I am looking at your boilers M.Is then 4.3 - "a variable duty pump should be set to give a temp diff of no greater than 20deg C"
"Important F&R pipe sizes - up to 18kw = 22mm, >18kw =28mm"
The flow rate required to provide 18kw @ 20 degC would main that your pump would loose approx 1M head just pushing that amount of water through the heat exchanger if you needed it full 30kw you would loose over 2.5Metres.

Your existing pump is a 5M head but that is the max it can push with no or little flow. Moving approx 0.215L/S it would only develop a pressure of approx 3.7M head, less the boiler 1M, would leave approx 2.4 M for the rest of the system. Not likely to be enough to overcome the resistance you have put in by re-piping in 10mm.
 
Fit a Grundfos pump with proportional pressure function? God knows, that's why I'm asking! Someone else must have come across this before?
Yes Chris thats why they were invented.
If you fit one would you need a by-pass ??
I don't think you do & have had my one at home closed for couple of years now with an Alpha 2 installed.
But if you do want to provide the minimum flow then why not use close coupled tees instead of LLH (to expensive) to provide hydraulic seperation. You are going to buy a new pump anyway so give it a go!!
 
Thanks, makes sense to me. Although is 3.5m head sufficient for the longest microbore to manifold circuit of 18m? My rough calculations would suggest not.
It's not just the length of the pipe which is important. You have to take into account the flow rate, which depends on the size of radiator and the temperature differential. For example:

Resistance of 18m of 10mm pipe connected to a 2kW rad with a 20C differential is approx 0.58m, with a 10C differential it is approx 1.94m. The flow rate has doubled so the resistance increases by four times.

Upload your rough calculations and I can take a look at them.
 
It's not just the length of the pipe which is important. You have to take into account the flow rate, which depends on the size of radiator and the temperature differential. For example:

Resistance of 18m of 10mm pipe connected to a 2kW rad with a 20C differential is approx 0.58m, with a 10C differential it is approx 1.94m. The flow rate has doubled so the resistance increases by four times.

Upload your rough calculations and I can take a look at them.
It's not just the length of the pipe which is important. You have to take into account the flow rate, which depends on the size of radiator and the temperature differential. For example:

Resistance of 18m of 10mm pipe connected to a 2kW rad with a 20C differential is approx 0.58m, with a 10C differential it is approx 1.94m. The flow rate has doubled so the resistance increases by four times.

Upload your rough calculations and I can take a look at them.

I won't embarrass myself as they are obviously wrong and too basic. It's plastic pipe too which might make a difference?
 
I won't embarrass myself as they are obviously wrong and too basic. It's plastic pipe too which might make a difference?
Not wrong just has advantages / disadvantages = smoother bore less fitting but at the end of the days it is a small pipe which limits the heat flow to each rad to something like 3 - 3.5kW but each is fed directly from a 22mm manifold.
 
To highlight a commonly held misconception that a differential pressure automatic bypass valve works well with a proportional pressure pump (e.g. Grundfos Autoadapt), please note that Grundfos does not recommend that the two are used together.
 

Similar plumbing topics

  • Question
With the system as it is at the moment, I'd...
Replies
6
Views
2K
I should have said "S-plan plus", of course!