The there is a couple of lockshields in the flow. How much to close and open them by? Off the top of my head upstairs are around 1/4 open and downstairs are a full turn open
I did advise adjusting the LS valve by 1/12 turn or less. Large changes, which you seem to doing, just makes it more difficult to get the system balanced. Most LS valves are fully open by 1½ to 2 turns from closed.
If you have recorded the current differentials for each rad, please post the info.
I did advise adjusting the LS valve by 1/12 turn or less. Large changes, which you seem to doing, just makes it more difficult to get the system balanced. Most LS valves are fully open by 1½ to 2 turns from closed.
If you have recorded the current differentials for each rad, please post the info.
If one rad is hot and another is cold I try to just turn it by 1/4 down and the other 1/4 up see if that changes anything but doesn't seem to be doing much.
I'll take the readings when I get in later and post.
Do you mean that the living and kitchen rads were literally cold, i.e. flow and return about 20C? If not what were the flow and return temps?
If the temperatures were so low, there is no flow through those rads. This could be caused by either an airlock in the pipes to the rads, or TRVs stuck shut, or by other rads robbing the problem rads of any flow.
Looking at the data:
Bedroom 3 is an anomaly with a flow temp of 75, which is higher than the flow at the boiler (72). All other rads are OK with a flow temp slightly below boiler temp. Are you sure about Bed 3 temps?
There is a large difference in the differentials ranging from 10C (Front Door) to 23C (Bed 2).
Yesterday to get heat to the down stairs rads I turned the bathroom and bedroom 3 trvs off. Turned them back on then started the heating strangely enough all rads are hot even the down stairs ones.
Just checked and the kitchen flow is 64 and return is 55. Living room is 64 flow and 44 Return.
Just checked bedroom 3 flow again it's now 70 and return is 56.