I dont understand the importance of what the manufacturers inlet pressure difference is really in your pipe sizing? It has no bearing on your gas supply design. It does not matter if there is no drop inside the appliance or a 10mb drop inside the boiler, your gas supply design would not be effected only your ability to confirm its suitability without additional test points.
with the TB's what they have done is inform engineers that there is a likely drop on there boilers between 0 and 1.5mb depending on the model (some manufacturers say upto 2.5mb). They have done this just to avoid confusion on our part as to what readings we get from the appliance inlet test point. This means for us engineers you can not rely on this test point to prove that you have the correct gas supply and the manufacturers are giving us the information telling us we cant rely on there test point. One reason for the tech bulletins i would assume is the high number of boilers the manufacturers attend under warranty and Gas Safe have noticed with undersized gas supplies and the number of engineers that in recent years have used these lower figures from the manufacturers as a reason not to correctly design and install the supply.
Gas safe in the WB TB have also stated that the gas supply must be designed correctly and suggests this can be confirmed by the fitting of a test point before the gas isolation valve.
Its not the manufacturers responsibility to enable the installer to confirm the gas supply is correct, tho i think it should be and i think they should be made to include a test point at the iso valve (but thats another argument). So in essence you as the installer are responsible for the gas supply, not the manufacturer and you have to be sure the gas supply is correct. You cant just test at the gas valve inlet test point and assume any drop over 1mb is down to the applance workings.
In my experience a very high percentage of boiler changes requires a new or upgraded gas supply, and i tend to assume if i cant see the gas run and the boilers not near the meter that i will be upgrading the gas. If you replace a boiler and find after testing its undersized then you will of course need to upgrade the supply. in many cases im putting 28mm in as standard. The problem is trying to explian this to your customer before hand so you dont have the discussion 3/4 of the way into a job.
you cant control what other engineers quote for and do, you can only do your job correctly.
why manufacturers cant give specific drops for each model i dont know? maybe its because of design variations? maybe it differs dependant of filter conditions? it would be interesting to know.