Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss baxi duo-tec 33 he a in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Messages
1,582
i serviced this boiler today and i done a gas rate, it came back on full rate at 2.25m3/hour ,- 21.69kw nett. looking at the mi the boiler should be running at 3.39m3/hour - 32.69kw nett . the thing is when i looked at the benchmark the figures the installer put in mirrored mine 2.25m3/hour - 21.69kw, any ideas
 
I'll be interested to see what this problem is, I had a vaillant last week with the same problem. Turned out to only be getting 9mb on full rate which cocked up FGA readings aswell.
 
would have a word with baxi tech its undergassing for some reason,gas valve fault,wrong jet/jet/burner restricted,i take it you have checked/ruled out fga readings under 0.004
 
fga results on max were ok but when on min they were a bit out and had to be adjusted,i;ll give baxi a ring and let you no how it goes
 
but that dont make it right,it dont make it dangerous either installer should have kicked it in when it was in warranty,did you do a full strip down service or fga readings only?
 
just fga ,i did not how ever complete service as i said i was not happy with readings and i would be back to complete.
 
be interesting what state its in when you strip it down,dont forget combustion gasket should be ok but advise custard a new one may be needed or just fit a new one anyway and bill accordingly
 
You could have a problem with the meter reg maybe? I suppose you could run it on full rate with the manometer connected to the inlet to see if the pressure fluctuates while in use.

Its a strange one this
 
You could have a problem with the meter reg maybe? I suppose you could run it on full rate with the manometer connected to the inlet to see if the pressure fluctuates while in use.

Its a strange one this
good call had that before,just thinking out loud restriction in gas pipe connection from gasvalve to burner possibly?worth checking anyway
 
might be a silly answer but isnt it just that the boiler might have regulated down the burner while you test it for an minute or 2, depending on meter ?
 
might be a silly answer but isnt it just that the boiler might have regulated down the burner while you test it for an minute or 2, depending on meter ?
should get full gasrate when flat out to dhw,meter should not have a bearing
 
i was thinking blocked hot water heatexchanger
 
Last edited:
Status
Not open for further replies.

Similar plumbing topics

(cont'd) Anyway, fairly keen for someone to...
Replies
2
Views
914
How did you get the valve sorted in the end?
Replies
1
Views
463
put the boiler on low very low and leave it...
Replies
2
Views
782
  • Locked
When your gas safe pm me and will re open it up
Replies
7
Views
2K
Yeah DuoTec offset, it was the Eco Elite that...
Replies
7
Views
3K
Back
Top