Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Bentone B11 burner always locking out. in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
I had a similar one with a sterling burner, as previously said I would have gone for the transformer. After the 3rd visit it turned out to be a ht lead partially blocking the photocell. Could have kicked myself for not checking first time

I thought on the ht leads & checked them when I examined the electrodes for cracks. The ht leads are a bit long but are folded away from photocell. In fact, I checked & thought just about everything. The boiler hadn't been touched & suddenly started this locking out. Nothing I have done has made any difference. I am happy to replace the transformer to test, but old one seems fine. I have been wondering if something is wrong with oil pump or it's stem, but this burner is only 3 years old & mechanically would normally be very reliable as you know.
 
Unfortunately, with this type of problem, you may have to diagnose by trial and error. Keep swapping things until you find it.

At least it locks out every two hours, so you should be able to fix it quickly, not so easy when the intermittent fault only occurs every week or two.
 
Short of air being pulled in I'd also be looking at the pump and the integrity of the pipework.

Another good one that caught me out once is debris in the tank that's too big to go down the outlet.
 
Couldn't you get the customer to ring you when they've reset it and then you arrive 1+1/2hrs later.

You'd only be in the cold for 1/2 hr or less.
 
Had a problem like this in the past with one of these. Talked to bentones man in Ireland. He said to change the motor. Did it and it worked for me. It was a similar situation to yours.
 
I went to the boiler later today with the intention of checking the oil pump etc & if all okay then either replacing the motor or the transformer as all else had been tried.
Luckily the boiler had been on a short time, so I first took a look at the spark & it was a lot different than previously - although consistently sparking, it was no longer a very strong spark it had been earlier tests. I have replaced the EB1 transformer in a few minutes & spent an hour & a half waiting. Hopefully that sorts it.
 
I went to the boiler later today with the intention of checking the oil pump etc & if all okay then either replacing the motor or the transformer as all else had been tried.
Luckily the boiler had been on a short time, so I first took a look at the spark & it was a lot different than previously - although consistently sparking, it was no longer a very strong spark it had been earlier tests. I have replaced the EB1 transformer in a few minutes & spent an hour & a half waiting. Hopefully that sorts it.

Eejit! You should've kept quiet! You know you've cursed yourself now! Hopefully you're right though.


Why haven't we got you in the Arms?
 
Eejit! You should've kept quiet! You know you've cursed yourself now! Hopefully you're right though.
Why haven't we got you in the Arms?

I will look an idiot if this doesn't solve it. I'll just never admit it! :smile:
Maybe some day I will join the Arms! Would love to know what goes on in that secret place. :grin:
Thanks to all of you for the advice! Just goes to show, if this works, never trust a transformer that gives a strong spark!
 
I will look an idiot if this doesn't solve it. I'll just never admit it! :smile:
Maybe some day I will join the Arms! Would love to know what goes on in that secret place. :grin:
Thanks to all of you for the advice! Just goes to show, if this works, never trust a transformer that gives a strong spark!

Got fed up waiting for you to get off your aristotle. I've put the wheels in motion for ya ;)
 
I keep a new EB1 in a case together with control boxes etc.
If it proves to have been the transformer, then I made the mistake of ruling it out because the spark (which I repeatedly tested several times on a couple of visits) was always very strong. Hard to know what approach would have been better, other than waiting for hours. Thankfully it is close to me.
 
Last edited:
I have come across these before when other so called engineers cant fix them so they tell the customer they need a new boiler.
hope it all works out best never easy these intermittent lockouts but we always get there in the end
 
Yes Kimbo, have seen a lot of fairly young boilers with brand new burners fitted where no doubt just a little part would have sorted the original burner. Or an entire new boiler as the customer probably is easy prey when they have an ongoing failing burner. I would always fix anything viable if cost isn't going to be close to a entirely new item. This time I wasted a few visits, but usually I don't take much time finding a fault - so really can't complain & I will stay easy going. :smile:
 
I didn't post on this as you know what your doing and I couldn't find anything that hadnt already been said, except have you done an FGA? Check its not over aired and blowing itself out.
Hopefully you fixed it anyway.
 
No worries Bunker, - I was only putting the question out there to see if anyone had came across similar problem.
I knew the combustion was fine, as had tested it after service & new nozzle, but it had been prior to that locking out. Burner is on a WB std utility boiler which I could set easily & firstly had been done by me at commissioning years ago. Boiler always started on press of lockout whether warm or cold start & co2 was I think above 11%, so was confident not over aired.
 
Last edited:
The posted problem is also a good example as to the fact that it is always a good idea to retain second hand burners from scrapped boilers as it can be far easier to swap a faulty burner (or parts from it) for a working second hand one to save messing about fault finding if you are very busy.
 
The posted problem is also a good example as to the fact that it is always a good idea to retain second hand burners from scrapped boilers as it can be far easier to swap a faulty burner (or parts from it) for a working second hand one to save messing about fault finding if you are very busy.

If it had been severe weather I would have swapped the burner. I have an old B11 burner would have done temp. I also have loads of electrical parts for them - better to have a second hand part than nothing.
Just an update on the boiler - no messages received, so the new EB1 transformer must have fixed it.
 
Just received a text from customer to thank me for sorting the boiler as it has been running fine with new transformer. Lesson is - don't assume a nice strong spark on several tests means a transformer won't fail intermittently.
Thanks for all the replies & help! :smile:
 
Glad you got it sorted.

Thanks Simon, - your first reply was spot on. You were lucky though! :smile: Let's call it an educated guess!
I did everything right, except i probably should have waited an hour at least, but just didn't find anything wrong.
Had one yesterday on a friends boiler - another EB1 but no spark & the back of transformer had a large blister. Seem to get a run of same things.
 
Did you change the control box too? Often this is caused by the box....cause and effect etc

On my friends boiler, I didnt replace the Satronic control box & that is a very good point!
He is an Electrician & had already diagnosed the fault himself & I let him get on with it himself.
I know that is a common thing on the Satronic boxes to do.
 
Status
Not open for further replies.

Similar plumbing topics

Coil.......................................plus...
Replies
1
Views
839
L
With no pressure gauge or flue gas analyser...
Replies
3
Views
1K
L
Camray 5 (90A) (20 year old) oil boiler, had a...
Replies
0
Views
1K
Lincoln22
L
Not worth the risk. She seems miffed at oil...
Replies
14
Views
2K
Well we agree on something
Replies
15
Views
7K
Back
Top