Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss bleeding flow and return from boiler to UFH manifold!! in the Boilers area at Plumbers Forums

Status
Not open for further replies.
J

John2008

Hi, I have just installed my Underfloor heating. 4 zones in total and pressure tested after filling each loop. I have now connected up to the 22mm flow and 22mm return (new install where the plumber who installed a new boiler left these ready for me). The current system have a radiator curcuit which works fine however the UFH circuait is isolated via a manual valve on the flow and manual valve on the return. Here lies my issue, I need to purge the flow and return from each valve up to the manifold (length of pope to purge is say 20m), how do I do this? The flow should be ok by isolating each UFH loop and simply bleeding the air in the manifold, how do I bleed/purge the return?

Any help would be fantastic!!
 
There will be instructions with the underfloor kit. Hose pipe is normally handy as well.
 
I've filled the actual ufh pipes as per instructions. I'm asking regarding the main flow and return from the boiler to the manifold as they are currently empty and isolated via valves next to boiler.
 
I've filled the actual ufh pipes as per instructions. I'm asking regarding the main flow and return from the boiler to the manifold as they are currently empty and isolated via valves next to boiler.

A picture of the set up would help?
 
Have you any air vents on the manifold? If so, just turn on the valves ( leave ufh off)
bleed air from manifold. ( make sure zone valve is manually open)
Re pressurise.
Turn on Any zone to make boiler circulate.( not ufh)
Bleed again.
Re pressurise.
Turn on ufh.

With that length of pipe there will still be some air, but will find its way to high points like towel rails and upper floor rads. These will need bleeding after a day or so.
 
Status
Not open for further replies.

Similar plumbing topics

You will need a check valve to stop reverse...
2 3
Replies
61
Views
7K
Thanks much appreciated , yes those isolation...
Replies
2
Views
769
Set the ufh mixer to 30-40 / what the design...
Replies
1
Views
2K
Check to see on which pipe the pump is on, the...
Replies
5
Views
2K
You've already spent thousands on a new boiler...
Replies
2
Views
954
Back
Top