Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Blocked return?? in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

Nick6588

Gas Engineer
Messages
35
Got called to a job as the WB conventional 30cdi was overheating and cutting out. Customer stated its been doing it on off at increasing frequency for about 2 months, a reset would sort it out. Now it won't run for more than 2minutes.
checked pump, pipes either side cold, pump burning hot, took off pump head and was rammed with debris and rusty lumps. I replaced entire pump.
problem the boiler now runs and will heat the hot water cylinder and two towel rads on primary circuit. Then cut out again after about 10minutes. If I turn heating on as well as hot water nothing heats up it just pipes until about 3m from hex.
Customer did say that they had personally dropped of 4 radiators for decoration purposes, I'm thinking maybe they dropped wallpaper or filler or something into empty rad then refitted it and pushed it into system.
Im thinking a power flush as it seems like a circulation fault? I don't have power flush equipment so use a friend as a subby who sorts it for me, do you think this is the way to go?
thanks Nick
 
or maybe just sludge i would try so cleaner in there first and see what the water comes out like
 
Im thinking a cleaner wouldn't get a chance to circulate if pump runs for a few minutes at a time, also it would mean leaving the boiler on to keep locking out every 2 minutes.
 
Im thinking a cleaner wouldn't get a chance to circulate if pump runs for a few minutes at a time, also it would mean leaving the boiler on to keep locking out every 2 minutes.

with a power flush it would/ override the pump
 
For me it would depend on access, certainly it's badly clogged so not sure a empty / draining would do much as it sounds badly clogged and the debris gonna need to be pushed out,
 
Check f n e tank make sure the lids properly on n tanks clear, ( if there is one and not been converted ).
 
I thought you meant just add a cleaner into system without power flush, sorry I mkisunderstood your answer shaun
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
'Have tried all off bar A, B, and C, so not...
Replies
3
Views
812
Thanks, I shall take a look in that case and...
Replies
21
Views
3K
Yep, that's what I meant (as per attached...
Replies
7
Views
1K
Replies
0
Views
448
I agree with Severn Trent. Since we don't...
2
Replies
25
Views
3K
Back
Top