Bravo33
The fault:
The boiler cycles on and off about every 3-5 minutes; Pump running continously with both hot water & heating in OFF cycle.
System:
Open vented; Worcester Bosch 24Si; Sunvic 2000 Pro programmer; Drayton cylinder stat; Grasslyn Thermio touch room stat; TLC TL MP3 mid position 3 port valve; pump.
History:
Moved into the house 6 months ago; Upgraded system of the past few years. Boiler installed 2005;
3 port valve, room stat, programmer, cylinder stat all new fitted within the last 6 weeks.
System drained and refilled approx 3 times with 2 replacement rads fitted and additional rad to the front entrance; system balanced and heat to rads working correctly.
The 3 port valve was changed as it would appear that it was sticking.
Further investigation showed the programmer was at fault as would not allow water & heat at the same time.
Cylinder stat changed as precautionary and appeared to be some 20 years old.
The system was re-wired last week as a precautionary measure.
Symptoms:
During the day the system seems to be stable however after the evening cycle with the hot water OFF at 18:30 and the heating OFF at 22:00 with this confirmed by the programmer indicator lights the pump is still running with temperature rise to the house thorughout the night.
I am getting up at 2am to switch power off to the system. Switch the boiler back on and reset it.
This solves the problem and the water and heat cycles appear to continue normally for the rest of the day.
The boiler cycles on and off about every 3-5 minutes; Pump running continously with both hot water & heating in OFF cycle.
System:
Open vented; Worcester Bosch 24Si; Sunvic 2000 Pro programmer; Drayton cylinder stat; Grasslyn Thermio touch room stat; TLC TL MP3 mid position 3 port valve; pump.
History:
Moved into the house 6 months ago; Upgraded system of the past few years. Boiler installed 2005;
3 port valve, room stat, programmer, cylinder stat all new fitted within the last 6 weeks.
System drained and refilled approx 3 times with 2 replacement rads fitted and additional rad to the front entrance; system balanced and heat to rads working correctly.
The 3 port valve was changed as it would appear that it was sticking.
Further investigation showed the programmer was at fault as would not allow water & heat at the same time.
Cylinder stat changed as precautionary and appeared to be some 20 years old.
The system was re-wired last week as a precautionary measure.
Symptoms:
During the day the system seems to be stable however after the evening cycle with the hot water OFF at 18:30 and the heating OFF at 22:00 with this confirmed by the programmer indicator lights the pump is still running with temperature rise to the house thorughout the night.
I am getting up at 2am to switch power off to the system. Switch the boiler back on and reset it.
This solves the problem and the water and heat cycles appear to continue normally for the rest of the day.