Boiler HW short cycling due to mixer tap | Boilers | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Boiler HW short cycling due to mixer tap in the Boilers area at Plumbers Forums

Messages
2
Hi. My boiler (a Vaillant Ecotec Plus 8xx) short cycle HW every few seconds and, because of the he priority it means no central heating. If I close the hot water circuit (turning the valve underneath the boiler) then the CH works fine. So, I can either have hot water or central heating.
The boiler engineer says there is nothing wrong with the boiler and the problem is caused by one of the taps in the bathroom or kitchen with a mixer (the shower is also a suspect).
My doubt is that the boiler short cycle happens even if no tap at all is open. It's not like we open the cold water and the boiler thinks there is a demand of HW.
Is that possible at all? It would be great if someone could confirm before I call other engineers and a plumber to find a faulty tap
Many thanks
 
If isolating the Hot water circuit stops the cycling then the problem lies within that circuit.
It can only be the Hot could be flowing into the cold via a thermostatic mixer or possibly the shower mixer if the Cold supply is from a storage tank.

Another possibility is a leak in the Hot circuit.
 
If isolating the Hot water circuit stops the cycling then the problem lies within that circuit.
It can only be the Hot could be flowing into the cold via a thermostatic mixer or possibly the shower mixer if the Cold supply is from a storage tank.

Another possibility is a leak in the Hot circuit.
Thank you for the prompt reply. That makes a lot more sense now. I fear it might well be a leak. Anyway, out to find a good plumber now.
Thanks again.
 

Similar plumbing topics

You will need a check valve to stop reverse...
2 3
Replies
61
Views
7K
Unfortunately the fitting of a new Venturi did...
Replies
3
Views
549
B
No the installers need to come out
Replies
10
Views
2K
So you don’t have any of the blending valves /...
Replies
3
Views
2K
Finally (I hope) got to the bottom of this...
2 3
Replies
55
Views
5K
Back
Top