Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Boiler Input-Output Efficiency Calculations in the Boilers area at Plumbers Forums

Status
Not open for further replies.
D

Damon Apple

Hi guys,

I am choosing to install in my project homework a worcestor-bosch 15i System boiler and i need to work out the
Input, Output and efficiency workings out on all settings.

I am totally stuck even after worcestor technical team sent me the installation data brochure but i just cant work it out.

This is what I am doing Max Rated Output=15kw
Max Rated Input=15.4kw

So i assumed output divided by input x 100 = 97.4% Gross efficiency and if i divide this by 1.11 i get the Net efficiency of 87.75%.

Now heres the problem worcestor bosch claim this has an efficiency of 90.1%

What am i doing wrong?

Link attached for the installation brochure instructions table etc...

http://www.worcester-bosch.co.uk/ca...r-i-system--manufactured--aug-09---jan-11.pdf

Any help very much appreciated :mad2:
 
This is what I am doing Max Rated Output=15kw
Max Rated Input=15.4kw

So i assumed output divided by input x 100 = 97.4% Gross efficiency and if i divide this by 1.11 i get the Net efficiency of 87.75%.

Now heres the problem worcestor bosch claim this has an efficiency of 90.1%

What am i doing wrong?
Nothing!

The efficiency figure in the manual is the "SAP2005 Seasonal Efficiency", which is calculated by a fairly complicated formula designed to simulate the usage of the boiler over a year. This has now been replaced by the "SAP2009 Annual Efficiency" which, for the 15i is 88.8%. You can read about this at http://www.sedbuk.com
 
Last edited:
<br>
This is what I am doing Max Rated Output=15kw<br>
Max Rated Input=15.4kw<br>
<br>
So i assumed output divided by input x 100 = 97.4% Gross efficiency and if i divide this by 1.11 i get the Net efficiency of 87.75%.<br>
<br>
Now heres the problem worcestor bosch claim this has an efficiency of 90.1%<br>
<br>
What am i doing wrong?

Nothing!

The efficiency figure in the manual is the "SAP2005 Seasonal Efficiency", which is calculated by a fairly complicated formula designed to simulate the usage of the boiler over a year. This has now been replaced by the "SAP2009 Annual Efficiency" which, for the 15i is 88.8%. You can read about this at Sedbuk
 
Status
Not open for further replies.

Similar plumbing topics

So today the 1.65gph nozzle finally arrived...
Replies
17
Views
3K
I also thought it was 10:1, for the 4000 and...
Replies
28
Views
3K
  • Locked
I have fitted a duotec in a few cupboards. And...
Replies
28
Views
8K
D
  • Locked
It's wired just as it should be (as shown in...
Replies
21
Views
4K
demiano
D
L
  • Locked
There are a number of issues here, all...
Replies
1
Views
2K
Renewable M
R
Back
Top