Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Boiler keeps on boiling water even heating is switched off

There is a blue wire in that box which is a neutral, probe with red meter lead on the orange wire and the black meter cable on the terminal screw where the blue wire is, meter set to 500/600v AC.
I tried the above, got nothing, I don't seem to have any power even though I switched back from the fuse box...

You can see from the photo there is no green light on the wilo pump...

Is there any other switch in the system?
 

Attachments

  • 16816536370205417591088217794894.jpg
    16816536370205417591088217794894.jpg
    353.1 KB · Views: 41
There should be nothing on apart from power as we are trying to determine.ine if the end switch is still made on the suspect m valve
 
OK then that's your problem then, just confirm that the CH and HW are both off??
What?? It itself is a problem???

I have now connected the orange wire back and measured at WC between orange and blue/neutral or yellow/green earth, both showing 240v

And I did it with boiler on, program for both CH HW off.
 
Yes, that is the problem, IE your M.valve is still sending a signal to the boiler/pump to run even though he M valve isn't getting a demand to open from the relevant system so needs renewing, more than likely just the actuator which doesn't involve draining down the system.

Why didnt you probe between the removed orange wire and earth with power on but both CH & HW off, it should have read 230V.
 
Last edited:
I agree with you conclusion, but base on the fact that this lever is loose.

Still trying to understand how my system is not powered up without having it to reconnect back.

I am thinking to replace the synchron motor, which I have learnt how to from youtube, seems like an easy job, and yes, no draining system need, although it is a challenge for me as you may see from my earlier photos, the faulty one is the one below and i can't even remove the housing completely.

Did a quick search on google for price and availability, what would be the difference between the 20 quids one from screwfix and 10 quids one from amazon? which one is a safe/wise choice?

1681655991225.png
 
Have never replaced the motor only.

"Still trying to understand how my system is not powered up without having it to reconnect back."
If you mean boiler/pump not running then its because there is no demand because you had removed the orange wire from the faulty M.valve, if you leave it disconnected and create a CH or HW demand then the boiler/pump will start up, is it a CH or HW M.valve thats faulty?.
 
Yes, that is the problem, IE your M.valve is still sending a signal to the boiler/pump to run even though he M valve isn't getting a demand to open from the relevant system so needs renewing, more than likely just the actuator which doesn't involve draining down the system.

Why didnt you probe between the removed orange wire and earth with power on but both CH & HW off, it should have read 230V.
Sorry, I did that, so i did measure 240V between the removed orange and the earth/neutral, while the connected orange in the box are reading 0V.

I was too focusing on why I cant turn on the system even though i had turn power on...
 
Have never replaced the motor only.

"Still trying to understand how my system is not powered up without having it to reconnect back."
If you mean boiler/pump not running then its because there is no demand because you had removed the orange wire from the faulty M.valve, if you leave it disconnected and create a CH or HW demand then the boiler/pump will start up, is it a CH or HW M.valve thats faulty?.
I get it now!!!!!

Thank you for being so patient to me!!!!!

Yes, I thought there were no power in the system, as I thought the green indicator on the pump means it is working/standby. I just disconnected the suspected orange wire again, turn on the system, boost hot water from the programmer to create demand, and boiler wakes up to work!
 
so I have swapped the synchron motor from a good one to the faulty one, it does not seem to help with the voltage, it still registers 240V.

So I need to replace the whole M. Valves?
 
so I have swapped the synchron motor from a good one to the faulty one, it does not seem to help with the voltage, it still registers 240V.

So I need to replace the whole M. Valves?
Yes, it’s not the motor at fault, it’s a microswitch.
 
The whole actuator, at least, , as its the spring return thats probably causing the problem or the end switch sticking on, remove the actuator from the valve and switch the zone valve on off with the actuator removed and see if 230v still present when switched off, also open/close the zone valve with a adjustable spanner or such on the valve spindle, it should move relatively very easily.
 
The whole actuator, at least, , as its the spring return thats probably causing the problem or the end switch sticking on, remove the actuator from the valve and switch the zone valve on off with the actuator removed and see if 230v still present when switched off, also open/close the zone valve with a adjustable spanner or such on the valve spindle, it should move relatively very easily.

Would like to try, but did a search on youtube, couldn't find any tutorial of how to, basically i have no idea what the structure is.

You know any good youtube video i can follow please?
 
which/where is this microswitch please? can it be replaced on its own?
It’s where the orange wire connects, but probably best to renew the actuator (valve head), some have replaced them, but I wouldn’t know how as I’ve never done it.
 
Have you tested if theres 240 on the brown for the 2 port valve in the wiring centre ?

With nothing calling eg heat and hot water timers off

You won’t get the head off as there’s not enough space to lift it out need to rotate the valve so the head sticks out front time for a plumber I would say
 
Now something I don't understand, I thought the system is actually running, but even though I boosted hot water, create demand, the boiler is not on, is always 00, I have only removed the faulty orange wire from WC, and touched absolutely nothing regarding HW, and I did see the boiler ignited yesterday for once (didn't check after), the time that I thought the system had no power.

So what is my problem now ...

When I press restart from the boiler, it doesn't seem to go through the usual start up sequence, but stays 00 all time...
 

Attachments

  • 16817195171525387490801073118752.jpg
    16817195171525387490801073118752.jpg
    216.7 KB · Views: 45
  • 16817197497376205304117597426368.jpg
    16817197497376205304117597426368.jpg
    174.4 KB · Views: 45
Last edited:

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Back
Top