Guys, many thanks. I think it's clear that the flow rate I had thought I was getting is well above the actual flow rate. Thanks for homing in on that.
As an aside, I should say that the heat pump is giving hot water in excess of 50 degrees, and the house is nicely warm via the UFH. (Not running DHW off this system.) So, I'm not unhappy with the system overall, but I am just curious about the actual COP compared to manuufacturers figure. Which is why I didn't initially go into lots of detail about the system. I just thought I would get a quicker answer about the COP calculation that way.
Nostrum: Good guess, in part! Yes, it's a Dream, no it's not a self-install.
So, my next move may be to try to find a heat meter, as someone suggested, since it seems I wont be able to work out an accurate figure using the Wilo display.
I can't work out what is wrong with my interpretation of the Wilo display. I'll check again when it is running. In the meantime here is a picture of it, showing how it displays the flow rate:
I fully accept my figure is wrong. From the pump curves I have seen, (it's a 1-4), I would expect about 1750 litres per hour, given that my head is 1.70 metres? Not quite the same as 4000 per hour......
As to DT being wrong, I'm not convinced. As I mentioned before, the inlet and outlet temperatures seem to be what I would expect.
As an aside, I should say that the heat pump is giving hot water in excess of 50 degrees, and the house is nicely warm via the UFH. (Not running DHW off this system.) So, I'm not unhappy with the system overall, but I am just curious about the actual COP compared to manuufacturers figure. Which is why I didn't initially go into lots of detail about the system. I just thought I would get a quicker answer about the COP calculation that way.
Nostrum: Good guess, in part! Yes, it's a Dream, no it's not a self-install.
So, my next move may be to try to find a heat meter, as someone suggested, since it seems I wont be able to work out an accurate figure using the Wilo display.
I can't work out what is wrong with my interpretation of the Wilo display. I'll check again when it is running. In the meantime here is a picture of it, showing how it displays the flow rate:
I fully accept my figure is wrong. From the pump curves I have seen, (it's a 1-4), I would expect about 1750 litres per hour, given that my head is 1.70 metres? Not quite the same as 4000 per hour......
As to DT being wrong, I'm not convinced. As I mentioned before, the inlet and outlet temperatures seem to be what I would expect.