Can a 12kw boiler ever heat a 4/5 bedroom house with 3 bathrooms? | Boilers | Page 2 | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Can a 12kw boiler ever heat a 4/5 bedroom house with 3 bathrooms? in the Boilers area at Plumbers Forums

Here's the factory in Derbyshire.
I wonder why the Vaillant and Glow worm are the same,, 😃

1664050478535.png
 
We have high bills ... in winter its 84 kwh a day for gas. But might that mean our current system is both inefficient and the ground floor cold.

Assume an average winter temperature of, say, 9°C and that you want your house at at average of 19°C that's 3.5 kW average for 10°C of heating. For the coldest weather (-10°C) you need more like 30°C of heating, which takes you to 10.5kW. So, maybe 12kW would be okay but, that doesn't leave much margin for error. It's also big step down in size from your current boiler. In your position, I'd want at least 15kW and probably 18kW just in case, which is the compromise others have already suggested.

Don't forget that if you have a terraced house, if your neighbours decide to leave it unoccupied in the winter for some reason your gas consumption will rise with the increased losses through the party wall. So you need a bit in reserve in case this happens.
 
Last edited:
Assume an average winter temperature of, say, 9°C and that you want your house at at average of 19°C that's 3.5 kW average for 10°C of heating. For the coldest weather (-10°C) you need more like 30°C of heating, which takes you to 10.5kW. So, maybe 12kW would be okay but, that doesn't leave much margin for error. It's also big step down in size from your current boiler. In your position, I'd want at least 15kW and probably 18kW just in case, which is the compromise others have already suggested.

Don't forget that if you have a terraced house, if your neighbours decide to leave it unoccupied in the winter for some reason your gas consumption will rise with the increased losses through the party wall. So you need a bit in reserve in case this happens.

Thanks for this summary advice ... I have been losing a bit of sleep over this ... plus the Mrs is from a tropical country so our house average temperature is more like 21.5c 😅 hopefully (probably) a 15kw or 18kw won't mean I need the 22 mm pipes being drawn from the front of the house so ... I'd like thank everyone on plumbersforums for reading and commenting ... it is much appreciated
 

Similar plumbing topics

Well the first thing i would be doing is...
Replies
6
Views
2K
Drilling joists is very rare and absolutely...
2
Replies
25
Views
3K
  • Locked
I'd go with a Vaillant cylinder with Vaillant...
Replies
11
Views
3K
walterwhite
W
Basically sounds like nothing was set in stone...
Replies
21
Views
6K
Back
Top