Yep
Low loss header
Then if the old boiler was running at ∆T 11°c the pump would of been capable of the higher flow rate and pressure required to overcome index circuit.
Sounds like this needs a low loss header and suitably sized secondary pump. The secondary side pipework will be ok in size but the new boiler internal pump isn't capable.
Alarming really as the installer really should have considered this 🤔