From an earlier post you indicated that sludge in the system had been dislodged by Sentinel X400. Do you have a magnetic filter on the system return? If so is it removing magnetite?

Before you replace the boiler, run it independently by opening the heating valve, bridging the thermostat input and running the system on the boiler stat. If ok, then address the control system issues.

The best approach is a simple logical process to find the gremlin. Initially, eliminate the boiler as the culprit. From your postings, I doubt it is the boiler, but sludge in the system does not help with the diagnosis. Eliminate this as an issue first
 
I managed to get hold of two plumbers. Entire three port valve and programmer is charged. None of the plumber checked wiring plan completely. They were more interested in changing above parts.
Since three port valve is changed water and central heating now work together.

The main problem remains that boiler keeps randomly switching on for a minute to two and water becomes v hot. I have called another plumber who can only make next Monday..

Apart from wrong wiring, what are the other reasons for this. Any other suggestions?
 
In view of what you told them about random boiler firing then i presume (if they were capable of changing the programmer and valve) that they would have checked the wiring at the boiler and pump to see if separately wired or if the boiler PCB is switching the pump or whatever, maybe its something as simple as the pump being wired correctly and the boiler having a permanent supply to its switched live.
 
In view of what you told them about random boiler firing then i presume (if they were capable of changing the programmer and valve) that they would have checked the wiring at the boiler and pump to see if separately wired or if the boiler PCB is switching the pump or whatever.
[/QUOT
In view of what you told them about random boiler firing then i presume (if they were capable of changing the programmer and valve) that they would have checked the wiring at the boiler and pump to see if separately wired or if the boiler PCB is switching the pump or whatever.
I was told that it doesn't have a PCB. It is with pilot light. Pump only gets on, when switched by programmer....
[automerge]1604153209[/automerge]
Pump can be switched on by programmer, even when the boiler power is switched off from plug on the wall
 
That implies that you have two incoming electrical supplies to the one system and the boiler is getting a feed from elsewhere. If this genuinely the case then you need someone with a good understanding of electricity to put right for you.
 
IF that is the case then it wouldn't be unheard of.
I learnt the hard way once when isolated what was thought to be the only incoming live to a system, I then touched what should have been dead only to get a shock.
I would have someone with suitable electrical qualifications to check it out and rectify.
 
A glowworm 50BF is a fairly basic boiler. It does not have a permanent live. As long as the mechanical pilot light is lit, when a live is applied to the boiler, it will fire and run until it reaches operating temperature. Thereafter it will shut off, turning on once the temperature falls below the set point level.

If the boiler is “randomly” firing that can only be because the boiler is receiving a live (+240v) feed and is below the set temperature.

If the boiler has been wired with a permanent 240v supply it will operate 24/7 switching off when it reaches set temperature and on again as the temperature falls below the set point.

In that configuration any external controls may operate the pump and open / close valves, but will not call the boiler for heat - the boiler is operating independently feeding the heating system when the pump runs.

You should not be replacing parts on a whim.

Any credible heating engineer should be able to diagnose and resolve the issue. A heating engineer that has not checked out the control wiring is not credible.

It is also important to know what the system is. Is it gravity hot water and pumped heating or pumped hot water and heating. If it is the latter has it recently been converted from gravity hot water? - That can cause a host of issues if not done properly.

At the end of the day, the boiler will only fire when it is in receipt of a live feed -so your Engineer needs to find out where it is coming from.
 
Last edited:
I was told that it doesn't have a PCB. It is with pilot light. Pump only gets on, when switched by programmer..
[automerge]1604153209[/automerge]
Pump can be switched on by programmer, even when the boiler power is switched off from plug on the wall

"Pump can be switched on by programmer, even when the boiler power is switched off from plug on the wall"
Are you saying that the boiler is just "plugged" into a wall socket?.
 
Thanks, this does clarify a lot about how the boiler and system works

We always had to run the programmer either mannualy or on timer, for hot water and CH. The pump use to come in both scenarios. No modifictions has been made to connections
[automerge]1604160066[/automerge]
"Pump can be switched on by programmer, even when the boiler power is switched off from plug on the wall"
Are you saying that the boiler is just "plugged" into a wall socket?.
Yes , it is. Here is the picture
"Pump can be switched on by programmer, even when the boiler power is switched off from plug on the wall"
Are you saying that the boiler is just "plugged" into a wall socket?.
Yes it is. Here is the pic of boiler
IMG_20201031_155905.jpg
 
Last edited:
If the above is correct the system is dangerous and needs to be rectified ASAP. I strongly suggest employing a decent electrician and heating engineer.
 
Hello all, the problem is sorted. There was an extra live red wire in the wiring box in the airing cupboard that was keeping the boiler on. The electrician checked and disconnected the wire. Wrong wiring was the case for around last 20 years. The boiler appear to have survvied this for so many years!!
Thank you for all the discussions here that enabled to point in the right direction....
 
Hello all, the problem is sorted. There was an extra live red wire in the wiring box in the airing cupboard that was keeping the boiler on. The electrician checked and disconnected the wire. Wrong wiring was the case for around last 20 years. The boiler appear to have survvied this for so many years!!
Thank you for all the discussions here that enabled to point in the right direction..

As myself and others pointed out right through this that boilers don't energise on their own, somewhere you had to of been getting this additional feed. Im glad its sorted.
 
It doesn't really matter now and can understand the boiler just firing on/off re that red permanently live wire but once removed would think that a switched wire from the wiring centre would have to be installed or re instated since the circ pump wasn't continuously running with the boiler.
 
Hi mate not sure if you corrected this, we had a similar problem with Glowworm boiler, after installation, new plumer came out and said the pipes too small, after spending much it still did the same. Turned out in the end to be the mesh filters on the input side to the boiler, output as well had dirt on them and stopped the flow, simple thing that any good plumber should check first. So take the input and output pipes off and clean the mesh fllters, maybe flush the system>
 

Similar plumbing topics

Off the sound of it I would say 15/50. Not...
Replies
1
Views
916
Np Simon. Hoping to get the boiler engineer...
Replies
4
Views
964
Ok great...really hoping it wasn't a leak.