Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Collapsed hot water cylinder in the Bathroom Advice area at Plumbers Forums

N

Networks1

Hello everyone

im new to this forum so I would like to say 'hello' and ask a question about a problem that has just happened with a horizontal hot water cylinder

there was a huge loud bang last night and the cylinder has imploded. At the time I had a wood burning stove on and just before the bang there was a loud grumble noise from the loft area. The cylinder has completely collapsed in and having looked on the web it would appear that this is not too common. Can anyone point me in the right direction as to what would cause this. I assume the heat from the stove must have been a factor but I'm guessing there should/ must be some sort of release valve that would usually prevent this from happening. The only thing that has been done to the system since I moved in two years ago is I had two pumps fitted by a plumber to help with low pressure on the cold an hot warer feeds. There are two pumps in the loft and it looks like one is connected to the hot water cylinder at the top in two places.

Many thanks in advance for any guidance with this .
 
Yeah, some pics would help, you can't automatically blame the last plumber for a couple of booster pumps fitted 2 years ago unless fitted incorrectly or in a dangerous manner.
The tank should have an anti syphon valve on it.
 
I shouldn't have thought that it had over heated as surly that would have exploded..

implosion would imply vacuum a negative energy perhaps. I've only ever seen this once and it was on a copper thermal store. Some one had bunged it to change a part stuck a drain hose on ans sucked the tank inward
 
This totally new to me - seen some balloned cylinders in my 30 years plus

Frankly I would be REALLY CONCERNED - thankfull no body was hurt and then really WORRIED about
the cause.

HETAS enginners are your 1st call and quite frankly who ever you used
last time - let him know and invite him to call by but GET A SECOND OPINION ANYWAY

chkING
 
Hello everyone

im new to this forum so I would like to say 'hello' and ask a question about a problem that has just happened with a horizontal hot water cylinder

there was a huge loud bang last night and the cylinder has imploded. At the time I had a wood burning stove on and just before the bang there was a loud grumble noise from the loft area. The cylinder has completely collapsed in and having looked on the web it would appear that this is not too common. Can anyone point me in the right direction as to what would cause this. I assume the heat from the stove must have been a factor but I'm guessing there should/ must be some sort of release valve that would usually prevent this from happening. The only thing that has been done to the system since I moved in two years ago is I had two pumps fitted by a plumber to help with low pressure on the cold an hot warer feeds. There are two pumps in the loft and it looks like one is connected to the hot water cylinder at the top in two places.

Many thanks in advance for any guidance with this .

Are you sure the cylinder was horizontal like the R101 ( strange) how can that function ?
 
Implosion would occur when cooling down as croppie said ... if pumping over occurred, was the expansion tank overfill outlet clear?! If the expansion outlet submerged and tank cools down the tank gets huge vacuum generally from the cold feed tank causing suction from the top and bottom of the cylinder.
 
Keen to see a photo of this. For it to sporadically implode, I'm thinking it's been plumbed up totally wrong and whatever vent it had got blocked. Needs someone to look at it in person. What area are you in OP?
 
Yep that's me.. living right next to the suicide bridge.. Erk.. but you can't jump off any more as tjey put anti climb spiky rollers you name it.. but the views from there are brilliant you can see all of London.. and yes I do work within the M25 London. Where you from. Pop in for a cuppa tea or beer when you're free..
 
spanner -just saw your address - Archway London - you must be £m doing plumbing inside m25

CHK
Nah its just like keep it up and running with another day. Working with a great gas engineer Imran, a clever guy knows his stuff and always helps me when available for technical issues.
Could not wish for anyone else.. YEHAA
 

Similar plumbing topics

  • Question
Has anyone fit the hot water cylinders with a...
Replies
0
Views
284
http://www.h2panel.co.uk/h2layout_a.htm...
Replies
1
Views
976
  • Question
Ya, they said the fact the anti-vibration...
Replies
6
Views
623
  • Question
Thanks for the replies. The 15mm pipe teed off...
Replies
4
Views
804
  • Question
It’s calling out for an unvented as it’s a...
Replies
10
Views
1K
Back
Top