And is that flue 2m below the velux?
600mm from edges of velux and 2m below
Draw a box 2m below and 600 either side if it's in that box it's a no go
3.20 Combustion appliances – removal of products of combustion
Figure 3.56
Obviously this is Scotland
cant have the flue protruding by 300mm anyway - unless they've changed it, then no white of flue to be showing.Here's a section - excuse the scribbled "computer writing". The flue is just long enough to give a tightest dimension to slate of 300MM
View attachment 26019
cant have the flue protruding by 300mm anyway - unless they've changed it, then no white of flue to be showing.
Being told previously by Vokera tech that the white is not uv rated and will rot over time if in sunlight but may have changed.that cant be accurate!
the flue on the vokera rear extension cannot be cut down less than ''375mm'' i think it is?
that means there will be white showing on non-cavity walls!!
Being told previously by Vokera tech that the white is not uv rated and will rot over time if in sunlight but may have changed.