I will get my thermodynamics book out again. What is the website you found that calculator on?
This was what I wanted years ago to give my own bathroom fan an over-ride function. Unfortunately Rapid Electronics had nothing of this sort and I didn't know where to look. I suspect this plus a separate non-timer fan would prove more reliable than rely on the cheap internal circuit of an all-in model, and at least when one unit breaks you don't need to change the whole lot. So thanks, Shaun. Next time...Analogue multifunction timer relays Selec 600XU-A-1-CU
Multifunction timer relays, analog, 13 time functions, 10 time ranges, 20-240 V AC/12-240 V DC, 1 x changeover contact, DIN rail mounting, IP20 protection, Screw-type terminals, Functions: On-delay/interval/flashing with off…www.automation24.co.uk
GEYA On Off Time Delay Relay ACDC12-240V 1xSPDT Multifunction Timer Relay 1SPDT | eBay
Output: 16A 1SPDT. 1 function of latching relay ( I ).www.ebay.co.uk
Something like this is what you need
Suppose should/must mention the qualities of steam for heating purposes where it is almost universally used in plants/factories normally at 8 bar which gives a temperature of 175.4C necessary for some processes.
As you are aware steam gives up its heat at constant temperature (isothermally) so if you compare a heating requirement of say 20Kw with steam vs hot water then only steam at a rate of 0.59 kgs/min (~0.6 LPM) is required as it gives up 2030.25 Kj/hr/kg (0.564 kw), if water heating is used then ~ 29 LPM at a deltaT of 10C will be required. Also steam heating reacts very rapidly to changing heating demands as its controlled on pressure, hence lower/higher steam temperatures instantly , the coil outlet is normally fitted with a float type steam trap which (traps the steam) will only pass water and ensures all the steam's latent heat is extracted.
I've wired the capillary stat in now, and as predicted it seems to be doing the trick just pumping round the circuit formed by the ABV.Excellent - I'll report back once I've wired the new stat into circuit next week!
Thanks, Graham
Yes. Actually, I have a feeling that it's also on its own circuit from the consumer unit (probably with a 15A MCB but I'm not at home so would have to check that) as well as the local switched spur which powers all the heating circuitry.Is the whole central heating circuit on its own 5 amp fuse and all wires come off that incoming supply?
I wouldn't have been surprised if it was spurred off the ring, but I don't think it is. I'll check the fuse rating in the fused spur tonight. I presume that 5A for oil rather than 3A is due to the starting current of the burner motor.It could be on its own circuit and more often than not people will spur off a ring main. If its got a switched fused spur then it's fine and will protect the system componentsin the event of a problem. Oil should be on 5 amps but could be a 3 amp fuse in place.
I wouldn't have been surprised if it was spurred off the ring, but I don't think it is. I'll check the fuse rating in the fused spur tonight. I presume that 5A for oil rather than 3A is due to the starting current of the burner motor.
Thanks, Graham
What is the stat setting and does it cut in/out a number of times before the boiler temperature stabilizes?I've wired the capillary stat in now, and as predicted it seems to be doing the trick just pumping round the circuit formed by the ABV.
I've put the extra stat inside the boiler cabinet and brought an extra permanent live across from the main junction box to power the pump bypass. In fact I haven't actually wired it in permanently yet as it occurred to me that I now needed to isolate both my new permanent live to the boiler as well as the existing switched live. I'm using a three pole isolator switch for this (the sort that are used for timed fans) in place of the current switched, fused spur. The whole installation is already fused elsewhere in the room, so I don't think that losing this fuse local to the boiler is a problem - unless you advise otherwise! I could put a simple fused spur outlet in as well if thought to be needed.
Thanks again for all your help, and the interesting diversion about steam thermodynamics - I haven't seen some of those terms since I was studying Physics at school which was a very long time ago
Graham
Hi everyone,
got to the bottom of the wiring for this relay should anyone else do one.
perm live goes to A1 with link to 15
neutral = A2
switch live to S
pump feed on 18
thanks for everyones help
The stat is set to about 90C (I'll explain the about in a bit) - I couldn't decide whether it was better to have it come on sooner and "waste" electric running the pump, but nip the overheat in the bud so to speak, or set it high so the pump only comes on when there's a danger of the overheat trip going off. So 90 was a bit of a compromise for now.What is the stat setting and does it cut in/out a number of times before the boiler temperature stabilizes?