Derek | UK Plumbers Forums | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Derek in the UK Plumbers Forums area at Plumbers Forums

Messages
5
Have installed new Honeywell T3r wireless thermostat to replace old 6360 unit. Old one was working fine but new receiver does not power up. Connected switched live to boiler to position A And live from programmer to position B. Existing neutral and earth sealed off. Put old unit back on works fine. Any ideas.
 
Sounds like you’ve only done half the wiring. The T3R needs a permanent live and permanent neutral and the switching wires. Depending on what boiler is installed, you could perhaps take the live from old thermostat (usually terminal 1), and the neutral (terminal 2) as your live and neutral, put a link wire from Live across to A and use terminal 3 into B.
 
Sounds like you’ve only done half the wiring. The T3R needs a permanent live and permanent neutral and the switching wires. Depending on what boiler is installed, you could perhaps take the live from old thermostat (usually terminal 1), and the neutral (terminal 2) as your live and neutral, put a link wire from Live across to A and use terminal 3 into B.
Thanks for that. The boiler is an old potter ton prima f on a Y plan set up so hope your reply still stands. Goes to show you can’t trust all videos on the net, the one I saw just used the two wires.
I will do what you suggest today and let you know how I get on.
 
No, that won’t work on a Y plan setup, as the live from the thermostat isn’t permanent, as it’s only livened up from the programmer. You’ll need to install the T3R near the wiring center, and either set the old thermostat to maximum (T3R would override), join the live and switched or remove wires from wiring center. If you’re struggling, post a photo of your wiring center and guidance can be given.
 
DB5F4F32-AD6A-403A-A248-1B3FA0DC4A85.jpeg
No, that won’t work on a Y plan setup, as the live from the thermostat isn’t permanent, as it’s only livened up from the programmer. You’ll need to install the T3R near the wiring center, and either set the old thermostat to maximum (T3R would override), join the live and switched or remove wires from wiring center. If you’re struggling, post a photo of your wiring center and guidance can be given.
No, that won’t work on a Y plan setup, as the live from the thermostat isn’t permanent, as it’s only livened up from the programmer. You’ll need to install the T3R near the wiring center, and either set the old thermostat to maximum (T3R would override), join the live and switched or remove wires from wiring center. If you’re struggling, post a photo of your wiring center and guidance can be given.
Attached photo of what I think is wiring centre in 1st floor airing cupboard. Can you make sense of all those wires?
 
Attached photo of what I think is wiring centre in 1st floor airing cupboard. Can you make sense of all those wires?
It’s not the easiest, but I’d say white (as it’s usual) with the yellow is the switched live from your thermostat, have a look at what colours are at your thermostat if Live out (terminal 3) is yellow, then I’d say they match. Then you might be able to do the same with the live feed (terminal 1). Neutral seems like all the blues together.
 
It’s not the easiest, but I’d say white (as it’s usual) with the yellow is the switched live from your thermostat, have a look at what colours are at your thermostat if Live out (terminal 3) is yellow, then I’d say they match. Then you might be able to do the same with the live feed (terminal 1). Neutral seems like all the blues together.
Yes, terminal 3 on 6360 is yellow. Terminal 1 is red . So, numbering the control box connections from the left ( ie. white and yellow is no 6 ) which no’s would you suggest go to where on T3r receiver
 

Similar plumbing topics

  • Question
Hi I have a Honeywell ST699 programmer which...
Replies
0
Views
659
  • Question
I wanted to bring this one to conclusion. My...
2
Replies
36
Views
3K
  • Question
Thanks, the installer had linked a permanent...
Replies
14
Views
2K
  • Question
Its a very ingenious but devilishly cunning...
2
Replies
25
Views
3K
Back
Top