Sorry guys can't really help without knowing how it's all been plumbed in !!
Multiple heat sources, as always buffer tank, / low loss headers. Flow rate always a killer with Heat pumps - whats the minumum allowed l/min?
We ALWAYS install, in line 30µm (micron) strainers and flow gauges in heat pump systems.
Had a call out not so long ago to a 'self install' - retrofitted and not flushed, he was getting low flow rate failures every 24 nours becasue the filter was blocking up every 24 hours!! - without the filter he'd have completely b**g**d the hex (ps. is that ** allowed any more Croppie? )
However I would have though that the Dream should have some kind of autodefrost cycle .. (usually steals heat from the buffer or heating system)
Multiple heat sources, as always buffer tank, / low loss headers. Flow rate always a killer with Heat pumps - whats the minumum allowed l/min?
We ALWAYS install, in line 30µm (micron) strainers and flow gauges in heat pump systems.
Had a call out not so long ago to a 'self install' - retrofitted and not flushed, he was getting low flow rate failures every 24 nours becasue the filter was blocking up every 24 hours!! - without the filter he'd have completely b**g**d the hex (ps. is that ** allowed any more Croppie? )
However I would have though that the Dream should have some kind of autodefrost cycle .. (usually steals heat from the buffer or heating system)