[FONT="]i all hope someone can help[/FONT]
[FONT="]I have an [/FONT][FONT="]150L hot water cylinder[/FONT][FONT="] with an immersion element after 1 hour it has consumed [/FONT][FONT="]2.69kW of electric[/FONT][FONT="] (im not too sure but I suspect the starting temperature was approx 42.9 degrees and reached 60 degrees).[/FONT]
[FONT="]Now when I use my boiler i measure the water temperature and its 42.9 degrees. After [/FONT][FONT="]1 hour of boost[/FONT][FONT="] on the control panel the water temperature has increase to 55.8 degrees so the temperature increase is [/FONT][FONT="]12.9 degrees[/FONT][FONT="]. According to a digital meter I have consumed 7kW however the digital meter does not show a decimal point so I ought to deduct one unit so the usage was at least [/FONT][FONT="]6kW[/FONT][FONT="] to heat my hot water tank.[/FONT]
[FONT="]From that data is it possible to calculate the efficiency rating of my boiler in comparison to using electric?[/FONT]
[FONT="]Also would there be a massive energy loss between the boiler and cylinder (the pipe is about 2 metres to the cylinder and return length approx the same) - its fully lagged.
[/FONT]I suspect I should use the formula:
Size of tank X 4 X temp difference / 3421 = Kw rating
150 X 4 X 12.9 / 3421 = 2.26
100 / 6kW X 2.26 = 37.6% efficiency rating
Does that make sense? it that the correct method?
[FONT="]Thanks in advance[/FONT]
[FONT="]I have an [/FONT][FONT="]150L hot water cylinder[/FONT][FONT="] with an immersion element after 1 hour it has consumed [/FONT][FONT="]2.69kW of electric[/FONT][FONT="] (im not too sure but I suspect the starting temperature was approx 42.9 degrees and reached 60 degrees).[/FONT]
[FONT="]Now when I use my boiler i measure the water temperature and its 42.9 degrees. After [/FONT][FONT="]1 hour of boost[/FONT][FONT="] on the control panel the water temperature has increase to 55.8 degrees so the temperature increase is [/FONT][FONT="]12.9 degrees[/FONT][FONT="]. According to a digital meter I have consumed 7kW however the digital meter does not show a decimal point so I ought to deduct one unit so the usage was at least [/FONT][FONT="]6kW[/FONT][FONT="] to heat my hot water tank.[/FONT]
[FONT="]From that data is it possible to calculate the efficiency rating of my boiler in comparison to using electric?[/FONT]
[FONT="]Also would there be a massive energy loss between the boiler and cylinder (the pipe is about 2 metres to the cylinder and return length approx the same) - its fully lagged.
[/FONT]I suspect I should use the formula:
Size of tank X 4 X temp difference / 3421 = Kw rating
150 X 4 X 12.9 / 3421 = 2.26
100 / 6kW X 2.26 = 37.6% efficiency rating
Does that make sense? it that the correct method?
[FONT="]Thanks in advance[/FONT]