Elevated tap problem | UK Plumbers Forums | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Elevated tap problem in the UK Plumbers Forums area at Plumbers Forums

Messages
1
I have a bathroom in my first-floor loft conversion. The header tank for the vented boiler is located as high as possible but the sink tap is just above the head of water so obviously the pump cannot self-start. A momentary activation of the bath tap overcomes the problem but it’s not very satisfactory.

A forum search shows that others have experienced this problem and the suggested solution is generally to raise the header tank. I cannot do this so have devised the plan shown in the attached diagram.

The pump is rated at 1.5 Bar, the Pressure vessel is rated 3 to 10 Bar. Presumably I can reduce the pressure a bit but will it work?
 

Attachments

  • ch.plumbing_26.jpg
    ch.plumbing_26.jpg
    36.6 KB · Views: 27
Switch to a negative / universal pump, doesn’t look installed correctly either

Also you want balanced pressures to any mixer taps
 

Similar plumbing topics

    • Like
  • Question
Ok thanks very much I will try that.