HiNo boiler will do that you should be able to change the perimeters of evo to adjust this
The default of the Evohome is 1 minute on time (max is 5 minutes) when it is in the cycling mode (6 timers per hour).Need to go longer else you will knacker your boiler as there designed to run longer
The majority of boilers only modulate 5 or 6:1 but yours is 10:1 so maybe to replicate these boilers increase the min output to 25/30% (5-A3) and see how it goes, can't do any harm. and can always revert.
Hi JohnI can't see any reason for a increase in gas usage, your house requires a certain amount of energy to keep it at a set temperature, the only reason that Evohome is range rating the boiler is to prevent too much setpoint room temperature overshoot?.
HiYour issue isn't the boiler as i've previously said. It's the on time rate from Evohome not working correctly, probably because of the algorithms it uses, thrown in with the fact it's been installed in a time when heating wasn't being used. Any boiler won't ramp up in 1 minute, Vaillants take about 2 mins to get going also. When you say the zone isn't meeting the set point, what temperature is the zone and what should it be?
I'd suggest deleting the troubled zone and resetting it back up. This will reset the learning for that zone. I'd also suggest looking at the flow rate to the rad, making sure the TRV on the rad is working correctly. Have you had all new TRVs throughout with the new EvoHome system?
Your multi room HR92s need to be set to Multi Room (Zone Configuration>Said Zone>Parameters>Single/Multi Room Zone>Multiple).Hi
I have set the on time for 3 minutes and the water will eventually get up to around 60 degrees after 4-6 cycles of the 3 minutes on/ 7 minutes off which at least lets the radiators get warmer now (it still spends a significant time on lower modulation and lower temp before hitting the 60 mark at the end of 3 minutes - after sevral cycles of it to get there).
The set temperature was 18 degrees, the Evohome said it was 17.5 and never previously got to 18. With the on time at 3 minutes it eventually gets there (after around 30-40 minutes of the cycling on/off).
That zone was deleted as a new HR92 was fitted on it but it still misbehaved until 3 minutes on time set.
There was also a new zone set with multiple HR92s (with one as sensor) but this has started to misbehave. When the hot water zone comes on, one of the raidators in that zone can also be hard on (gets very hot) and the temperature ramps up (read with a min/max temeprature unit) from the set point of 18.5 degrees to 21 but the zone says it is still requesting heat (all the other HR92 units in that zone are cold) and thinks the read temerpature is 18.5 even though clearly it is not.
I had this in the recent past (as new system) when there were 6 radiators in a zone but when the zone was split, a HR92 was replaced as it was thought to be the cause. I have tonight changed the HR92 with another radiator in the zone to see if it follow the HR92 or remains at the radiator.
Now the installer says that my zone with multiple HR92 units cannot be set to multiroom (can only be used single room) as the person he contacted at Honeywell says that my system cannot do this (I have had no explanation as to why).
Thanks
Colin
HiYour multi room HR92s need to be set to Multi Room (Zone Configuration>Said Zone>Parameters>Single/Multi Room Zone>Multiple).
Advanced Load Scaling> Is this set to None?
Swapping HR92s will only confuse the learning, but you can give it a try.
You also didn't answer my question regarding the TRVs, are they new valve bodies or existing?
Is the Evohome system been installed new with the boiler or existing.
Thanks, I think I'll need it. (hoping the system will not be 3 minutes on/ 7 minutes off for the rest of the night as may be tempted to turn the boiler off.It's not hard to change it and try it, but so be it. Wait for your reply.
Good luck getting the system sorted.
Thank you for your help and assistance.It's not hard to change it and try it, but so be it. Wait for your reply.
Good luck getting the system sorted.
Your house must require some level of heat to keep it warm so even though you are not seeing any rise in room temp this just proves in a way that the evohome is working by just firing the boiler long enough to keep the house exactly at your required temperature by keeping the rads at the required temperatures.Thanks, I think I'll need it. (hoping the system will not be 3 minutes on/ 7 minutes off for the rest of the night as may be tempted to turn the boiler off.
I have set to multiroom on this zone to see if anything changes.
Hi JohnYour house must require some level of heat to keep it warm so even though you are not seeing any rise in room temp this just proves in a way that the evohome is working by just firing the boiler long enough to keep the house exactly at your required temperature by keeping the rads at the required temperatures.
Except that your rads are at the room temperature then they must be emitting some heat so even if they are only at 25C and the rooms temperature is 18C then they will still emit ~ 8% of their rated output say 1.6 to 2 kw of a 20kw rating which isn't going to break the bank.
Hi JohnYes, understood, but Evohome seems to be saying so that as long as the the room temp is within 1.5C of its setpoint that whatever minimum time you have set is in fact a fixed time and not just a minimum?. So if the temperature offset is 0.75C then the controller just looks for the TRVs to be open say 50% or something like that and during this x weeks learning curve if the room temperature isn't rising then it might look for 75% opening or whatever but has no effect on the actual run time?
Is this your understanding of how it works?
HiAnother evohome user here, been reading this thread with interest, I do believe when evohome is doing this TPI thing (eg firing for 1 minute in every 10), the flow temps are not supposed to get up to anywhere near what you'd expect, it's literally just warming the water slightly to dump a small amount of heat into that zone, the idea is to prevent an overrun.
My system seems to work quite well as it will maintain the temps in each room once the set point has been reached. However what I did find is that some rads did not get warm at all despite calling for heat. It seems than for low demands of 10-20% when the boiler is firing as per TPI schedule, the valve does not open enough inside the TRV to let any water pass, I found that on a couple of rads I had to set the HR92 stroke parameter (setting 6) to 1. That seemed to fix the problem and even on low demands I can feel some heat in the rad, it's not hot just warm..
I don't think anyone has mentioned this so give it a try.