Top stuff, thanks steve! when you mean turn boiler off, can i just set the system to frost setting i.e 5 degrees C. as i don't fancy turning it off at the wallin case i can't get it started again, especially as it's gone cold again.

Thanks again!!! really appreciated
 
Because by isolating the boiler you have in effect reduced the water content that the guage is measiring to just a few litres. If the leak is in the heat exchanger the guage will drop quickly, so your boiler should not need to be off for long
 
Will do! Pity you not in south wales, i'd commission you to sort it out 🙂
 
Hi, have not had a chance yet, been away with work, But will get on with this, this weekend.

Also i'll get that diagram sorted also.
 
I have exactly the same problem as soon as i switch the hot water on the prv lets water out the top of the tank, i have noticed that on one of the expansion tanks (the one with the gauge)a tap to it is switched off, does this need to be on?
 
Hi, no the tap i assume is the filling loop to top the system up. This is the original problem i had and has since been corrected, some pipes were installed the wrong way. You could also have a faulty PRV - I think they are set to release (open) at 3 bar pressure - check the gauge and see if it goes up passed 3. You'll prob have to let the heating and hot water be off for 4 hours and refill with the loop to get the gauge back to 1 bar (or what ever it should be).
 