White, Blue, Grey & Silver (stainless steel) = wholesome / potable water usage. (or so it use to be)
Red = Heating (or so it use to be)
It was all to do with the type of rubber used, I seem to remember that natural rubber was used in potable as it didn't support bug growth but they couldn't handle high temperatures so neoprene was used for heating.
My understanding is the same as Best, manufacturers (some at least) are moving over to red for everything because of the newer types of rubbers used, so we will all need to start checking the reds on potable systems before condemning the original installer.
My advice see if they have a recommended technician
The expansion vessel won't be the source of your problems, any air that does end up in it from the CH water doesn't cause any issues as it acts in the same way as the air behind the bladder, there's no way you'd get enough air in there to alter the performance of the vessel and it wouldn't cause any noises.
With regards to the having to constantly bleed your rads, is this a new system? Have you had any alterations made to an existing system? Has an inhibitor been added?
I know this is quite an old thread now but have you actually had a plumber out that deals specifically with system design
How old are the radiators? are they gassing out? when you bleed does it smell like rotten eggs? Are there any auto air vents as these can sometimes allow air in too?
Constant air ingress is sometimes caused by a poor seal on the vacuum side of the pump. I think I've posted this before but I did an experiment with some clear hose connected to a circulating pump and put in a fibre washer with a scratch across it on the vacuum side of the pump. Whilst it never leaked water it did show a stream of bubbles being pulled into the system when the pump was running. This air would then usually move to a high point e.g. upstairs radiator. The air ingress was stopped by the installation of rubber pump washers.
I made this setup in the workshop because someone did not believe air could get in at the pump without showing a leak when the pump wasn't running. I proved it can! Worth a look checking the washers at the pump, tighten them if possible or replace them with rubber ones if they aren't already. It's worth a try!
Hi Guys,
I have a caleffi PRV in my hands, to replace the current one, as when heating the system the gauge doesn't move.
- it does appear to move correctly, when pressurising via cold feed.
Before I went to replace the PRV, I had a quick look at instructions...
In bold text it states do not install upside down...
Well the current one is upside down, I slapped my forehead and growled!
So the question is, what are the consequences of installing the PRV upside down? Am I going to need to repipe this?
I'm surprised as no one said the original was upside down, so perhaps the instructions are not great?
Please left me know as I'm sat here with the heating off and drained down wondering what to do?
Thanks.
Richard
As per the picture on the original post, the pressure relief valve that is below the expansion vessel.
The heating wouldn’t need drained down to replace that valve. 😵
Could you have a leak somewhere ?
If the system is pulling in water you will keep getting air. I'd also check pump connections which can also pull in air on each start up.
I would try shutting off the automatic air vent, have been known let air in. If you are bleeding radiators that octen it is not doing its job anyway.