Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Ferroli 901 short cycle in the Central Heating Forum area at Plumbers Forums

Messages
23
good evening, I've got an issue with my ancient however well maintained ferroli 901 boiler, it short cycles, it stays on for 35 seconds, then shuts off for approx 10 seconds and repeats all day, this never happened last winter, just this winter since turning it back on.

When turned on is fine, however after approx 10 minutes when up to temp issue starts

This is what I have done so far,


2 new thermisters.
New pcb
New flow meter

Water runs hot / cold, however this is due to the short cycling

I have been told as soft water area unlikely to be heat exchanger.

All rads are warm all over,

No airlocks in rads or taps.

Pump is working well because rads get hot quickly.

Any ideas please, I would appreciate any advice,

I appreciate ferrolis aren't the best
Thanks
 
Changing the thermisters was probably your best stab.
If that didn't work, I wouldn't have changed the PCB or Flow Meter.

I would have started to look elsewhere and determined what was causing the problem.
Gas rates, pressure switches, flame rods, flame sensors, pump capacitor, gas valve, gas valve modulation, heat exchanger.
Most of these things can be checked within a very small amount of time.
 
ive figured it out, however I need a bit of advice, it's the pump, it's got to the point now where it's not even starting up, I've tried to remove the old pump, however the switch and casing come of but how do you get the actual fan bit out, thr shaft with the rotating part won't come out of the cast iron casing, how do I get it out?
 
ive figured it out, however I need a bit of advice, it's the pump, it's got to the point now where it's not even starting up, I've tried to remove the old pump, however the switch and casing come of but how do you get the actual fan bit out, thr shaft with the rotating part won't come out of the cast iron casing, how do I get it out?
 

Attachments

  • DSC_0085.JPG
    DSC_0085.JPG
    182.9 KB · Views: 36
Have you drained the system?
 
yep, systems empty, is this part supposed to come off, I don't want to have to buy the whole cast-iron part unless I have to, can I tap this with a rubber hammer, surely this should come out, there's nothing on backside of It securing it. The replacement part has it all as one piece
 
Yes if empty / drained Waco with a hammer
 
afternoon, I've got a further query, I managed to get the original pump off, it was rusty and the plastic parts looked like rusted metal there's what appears to be a ceramic collar in there which had bits chipped off, I've cleaned it all up, bearings have gone I think, however it still spins, I've put it back in until new one arrives and no more short cycling, however, ( sigh) the heating comes on and the water is now at a constant heat but it is a lot lower that before. I imagine that the current pump isn't woring to full capacity, could that be responsible for this, I haven't replaced aw nything else. I'm hoping that the new pump will spin more freely and solve this, although I thought the pump had little to do with water temp, any advice would be appreciated. Thanks
 
Ok. I've got a problem, I'm hoping it's just a faulty part, my new pump came today, I installed it ( I've done a few before with no issues) it ran for about 5 minutes and then started smoking, ( literally) and then blew the fuse I took it out again and it's literally melted. The inside of it has burnt out, any idea why this would have happened?, even the previous one I took out didn't melt? I am hoping it's faulty, I can't see how I can be at fault with this?

Thanks in advance
 

Attachments

  • DSC_0089.JPG
    DSC_0089.JPG
    214.3 KB · Views: 26
If you’re confident you wired it up correctly and with no loose connections then they will replace under warranty

Was it the correct voltage rating? (A 120V motor on a 240V supply behaves rather like you described...)
They were both 230v, I've complained to the company and they want me to send it back at my expense to be inspected, I've asked them if they can send another for tomorrow and I'll send the other back, they said, " no"!! . So I've bought another one from someone else and am going to ask for a refund, I hope they don't give me any nonsense or I'll go down the route of "my house could have burnt down "
 

Similar plumbing topics

I have an ancient ferroli 901 optima that due...
Replies
0
Views
505
B
No the installers need to come out