Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Firebird oil boiler, black smoke problem in the Boilers area at Plumbers Forums

Status
Not open for further replies.
R

Robster0303

Hello guys, new member here. I have a firebird oil boiler. It has worked fine up until a few days ago. There was black smoke coming out the flue and there is a build up of soot inside the vent. Can I clean this myself ? Will I need a specialist to sort it. I have turned the system off now as I am using an immersion heater for now, but obviously we have no heating and its gonna get cold in the next few weeks.

Thanks for any help/info much appreciated

Rob
 
Yes get an OFTEC guy in, the boiler will ned to be cleaned and nozzle changed, pump pressure checked also flue gas readings may need to be adjusted etc. You will not be able to do these things on your own. You may want to clean it out yourself and you may be lucky but something has caused it to go sooty and only an experienced engineer will be able to find what it was.
Basically soot is unburnt fuel.
 
defo a oftec guy needed it could be a faulty wrong size nozzel wrong pump pressure sooted up baffles etc etc
 
Okay guys thanks for your replies. I will get someone in then. I wanted to do it myself to save on the pennies but safety first....so thanks again guys !!!
 
if only there were more like you robster that werent willing to risk there lifes and others for a sake of a few quid. where are you located
 
yup go to Oftec's website and find one of us Oftec Engineers :) should be a simple fix as previously mentioned, however he will need to look into the causes of the soot build up, which as mentioned above is probably due to incorrect O2 amount and maybe an incorrect nozzle fitted. The oftec engineer may well want the original boiler manual if available too.

:)
 
Status
Not open for further replies.

Similar plumbing topics

All fixed. Changing the nozzle and cleaning...
Replies
4
Views
552
They claim 120L available at 20LPM at a 40C dT...
2
Replies
27
Views
3K
External hounsfield heat only. If you really...
Replies
4
Views
1K
Thanks much appreciated , yes those isolation...
Replies
2
Views
781
Back
Top