Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Flue bracket regulations in the Plumbing Jobs | The Job-board area at Plumbers Forums

Messages
37
The flue runs up from the boiler into the attic. There are then two 45 degree elbows before the flue runs out to the rroof.The flue runs parallel from the boiler to the bit going out of the roof with an angled bit in-between. Where by regs should the brackets go and how many will be needed?

IMG_20190327_174332.jpg
 
I only went to look at the flue today .It was serviced and the owners were advised to add brackets to bring it up to regs. Whoever serviced the boiler didn't turn it off and allowed it to run as it has been since it was installed a few years ago.

IMG_20190327_174643.jpg
 
I'm not gas safe registered. I went to do a few other jobs at the house and was asked about the flue brackets whilst I was there. I said I'd ask and see exactly what needs doing.
 
That’s not what he said, plus why would you anyway? Doesn’t give off the right impression in my book, spend a few quid more and the job is bob-on.

Right = Right.
 
Depends how it is ran. I would never use it. But if it done correctly it should be fine.

Needs to be manufactured approved method strap banding isn’t
 
I’m sure I saw a bulletin some where that said as long as it goes around the flue and is tight to opposite beams it is ok. I’m not that bothered anyway as I always use Worcester flue brackets. I was just saying that I’m sure I saw it somewhere.
 
Strapping is not allowed.

You need a bracket on each stretch as a minimum

You also should have a bracket at the top, as it exits, in addition to the others.

So, technically, 4 brackets as a minimum.

The whole structure must be perfectly rigid, otherwise more may be required (speaking generally, probably not an issue in this case)
 
Also had two Gas Safe inspectors just recently tell me the same thing, Strapping is not allowed and has to be a proper flue clip on every length of pipe. We've always used clips anyway as I hate the strapping so didn't matter, but i've seen many that have been strapped.

My view is that if you go to a job that's old and it's strapped and adequately supported & secure then it's fine. But on any new installations they should be flue clips.

Getting back to the OP, needs 3 clips on that flue.
 

Similar plumbing topics

It might be, if it can't be rectified by...
Replies
6
Views
439
Yes these can be converted to any type of...
Replies
2
Views
556
T
Do a slightly dodgy job and let the extractor...
Replies
3
Views
990
I took those photos! Looks like the only...
Replies
9
Views
1K
Hi, thank you for the reply. It's confusing...
Replies
2
Views
722
Back
Top