routine service today on a ecotec pro 28 approx 8 years old. Basically the boiler would only stay fired up for about 45secs before cycling on and off on max rate. This wasnt long enough for me to get an accurated fga reading.

Gas rate and pressure was good. Am i right in saying could potentailly be a plate hex partial blockage?
 
So it wasn't a service it was a breakdown :p:p:p:p

Does it do it on heating as well as hot water?
 
routine service today on a ecotec pro 28 approx 8 years old. Basically the boiler would only stay fired up for about 45secs before cycling on and off on max rate. This wasnt long enough for me to get an accurated fga reading.

Gas rate and pressure was good. Am i right in saying could potentailly be a plate hex partial blockage?
How was the gas rate and pressure good if you cannot get it into max rate?
 
Did you test with the hot tap open ?? Normally test mine with a bath or kitchen tap

Had a basin overflow ooops :D
 
So it wasn't a service it was a breakdown :p:p:p:p

Does it do it on heating as well as hot water?
No no. It was a service. 45seconds is enough time for me to check gas pressure pal.... And i checked gas rate at 1/2ft3/rev and it was all good.
 
Yeh bath tap on full in max rate boiler kept vutting out around 45 seconds.

Yea plate fecked then check on heating first maybe main hex
 
No no. It was a service. 45seconds is enough time for me to check gas pressure pal.. And i checked gas rate at 1/2ft3/rev and it was all good.
No worries mate. I like mine for at least 5 minutes on full rate before I do anything. Don't want anything biting me in the bottom later on. Definitely sounds like a circulation issue.
 
Yea plate fecked then check on heating first maybe main hex
I agree mate. That's what I was saying.;)
If it is the main heat ex. Quote a new boiler. I passed a job to vaillant for a one off repair the other day and the cheeky beggers sold my customer a new boiler because they couldn't get the side panel off as riveted. I went blooming mad at them. I was not a happy bunny.

Edit due to wanting a rant
 
I agree mate. That's what I was saying.;)
If it is the main heat ex. Quote a new boiler. I passed a job to vaillant for a one off repair the other day and the cheeky beggers sold my customer a new boiler because they couldn't get the side panel off as riveted. I went blooming mad at them. I was not a happy bunny.

Edit due to wanting a rant

:D it's been a long day looking at carpet

Could you pull the hex out and clean it ? How easy on the vaillints ?
 
:D it's been a long day looking at carpet

Could you pull the hex out and clean it ? How easy on the vaillints ?
Really easy if it's a combi. The reason I passed my to vaillant was the price of a new heat ex is extortionate. (Or so i thought, but cheaper then a new boiler). I have had one out and back in again in 2 hours. When I changed a flue collector.

On an vented though. Not a combi
 
Will check it on heating, if all good will pull the plate out and try clean. Yeah the main hex on vaillants are like £500 before labour haha.
 
if you put it on P1 for max you need to check all TRV's are open , opening tap makes no difference on the vaillant if hot flow is poor ;)

if boiler been oversized you can either take diverter head off and pull the pin out to mid position with pliers or turn boiler off at spur and while the diverter is moving at start up pull the electrical connection from diverter at mid position , then put into P1 max which makes it go round the heating circuit
 
Status
Not open for further replies.

Similar plumbing topics

Was re-checked and passed no ID. pressure 15.5mbar
Replies
57
Views
14K
I have connected the secondary pump to a wifi...
Replies
9
Views
2K
H
Hi there, thanks for your time to look at this...
Replies
0
Views
909
HRP123
H
Incoming 7degrees, raised by 33 degrees. New...
Replies
14
Views
7K
B
Bypass open too much? Close it down and open a...
Replies
14
Views
334
Back
Top