Steve, they normally they come with 2 fibre washers, 1 for each side of the ally elbow
 
Taper thread on to parallel thread with paste or unsintered PTFE ok. Parallel thread on to parallel thread is a definite no no unless you have a washer.
 
one thing to remember is that even tho the manufacturer may state its ok to use a flexible hose the hose must not be exposed to high temps and hang free and with no strain. So if there is a oven fitted underneath you must be certain that the hose does not touch a hot part of the oven or get to hot in the void space, or get put under strain. As most ovens use this space as a vent/cooling route i would say that your better going with copper to be sure.
 
Lovely stuff image.jpg:)
 