Always thought the bonding to a gas meter was max 600mm from meter. Electrician today has said "or" where the supply enters the building if the pipe enters the property away from the meter.
 
Spark is correct.
Within first 600mm from meter before 1st tee or at point of entry into property.
 
Spark is correct.
Within first 600mm from meter before 1st tee or at point of entry into property.

Ok, thanks. Is this in bs6891 do you know? Or the standard for meters bs 6400-1?
 
Last edited:
Ha ha it's a myth never happens anyway
 
inside is better normally as long as its visable otherwise the next engineer along with notify it as not bonded.

im supprised you have come across a sparks who knows the regs, i told the sparks on site today you cant enter a meter box from the back with his earth cable (drill a hole where he likes) and he looked at me like i was talking out me hole. Wont think that way when the grid want £1000+ to change the box tho..........
 
Last edited:
I love the way the 2 set of reg bodies talk to each other :)
 
inside is better normally as long as its visable otherwise the next engineer along with notify it as not bonded.

im supprised you have come across a sparks who knows the regs, i told the sparks on site today you cant enter a meter box from the back with his earth cable (drill a hole where he likes) and he looked at me like i was talking out me hole. Wont think that way when the grid want £1000+ to change the box tho..........

I take it thats a built in meter box. Why can't he come through your sleeve with your pipe? :)
 
BS 6891 section 8.16 figure 9. Preferred location at point of entry.
 
Status
Not open for further replies.

Similar plumbing topics

It can actually throw you across the room! If...
Replies
4
Views
459
Thanks for the advice!
Replies
2
Views
656
Yes, for 20p it'll save the mess and you can...
Replies
13
Views
369
The only opening in a built in gas meter box...
2
Replies
42
Views
8K
you will have to call the gas transporter /...
Replies
1
Views
927
Back
Top