ok i think that has uploaded ok.

It's clear to me as i have seen the job, any questions please ask.
 
Without even working that out, it needs 28mm.
 
I will have to come back with that info.

This is where my lack of experience shows, will need to get my head in back in the books.

If the boiler is 24KW and the cooker is about 8Kw, you are good to have it in 22.
 
Yeh im sure your right.
But its showing ash to refresh his memory

Phil's right, instead of throwing pipe sizes at Ash it'd be more beneficial to him to help him with the working out for future jobs. I know most of you can get it right by rule of thumb and experience but our boy's not quite there yet.

Let's make a good engineer into an excellent one.
 
Phil's right, instead of throwing pipe sizes at Ash it'd be more beneficial to him to help him with the working out for future jobs. I know most of you can get it right by rule of thumb and experience but our boy's not quite there yet.

Let's make a good engineer into an excellent one.

I’ve done all of the math just now on paper. There are could be more bends and elbows though.
 
Ok so lets say for arguments sake it does definitely need 28mm.

That would be 28mm from the meter and only reduce it at the points it branches off for each appliance?

I'd say 99% of houses I go to it's 22mm off the meter all the way to the boiler and 15mm for cooker/hob. I rarely see 28mm from the meter!. I should get back to this property tomorrow and will check the appliances. As it's all in 22mm now does that mean it's all been incorrectly sized up to now or does moving the meter 4 meters away and adding in a few 90's make that much more difference?

I'm happy to do it the correct way but it's frustrating thinking how little I see 28mm on peoples houses if this is the case. Thanks for all the replies.
 
Last edited:
Ash. If its 4m longer and you have 2 branches/legs.
That 4m can then effectively becomes at least 8m or with an elbow etc more...
It Can make all the difference...

...especially when its being audited by gas safe.

I cant see diagram as on tapatalk and its not showing
 
Ok ill check KW of the appliances when i next go back. If 28mm is required that's what i will advise. I know the customer is not going to want me to upgrade the whole lot to 28mm but if that does turn out to be the case he will have to go elsewhere. I might be lacking experience but that's why i come on here and ask questions. I know some guys who would have just extended the 22mm no questions asked.
 
Is it correct that the entire run would have to be 28mm? (not counting the reducing down for the appliances)
 
I will check appliance kw asap then i will know for sure. thanks guys.
 
if they are all working ok now if you put 28 from meter to existing youlll be fine it loks like your loosing 1.5 of 22 up to existing meter so only adding 6.5 stick it in in 28 if the appliances are low add a bit more but i doubt there would be a problem
 
My personal opinion would be to run the new pipe in 28mm under the floor even if it didn't need it. My reason would be that there boiler in at the moment is probably ok off it now but if in the future they want it ripping out and a nice big combi installing then chances are they will have to upgrade the gas to cope, so as someone has already said it's just future proofing it and it will be cheaper and easier to do it now than having to rip up floor boards etc in the future. I would explain to them why you want to do it like that and most people would probably go for it.

As for your question about why you hardly ever seen 28mm is that a lot of new boilers installed the gas pipe is undersized, people just put them in and not think of the gas pipe they just see 22mm pipe and a 22mm connection and connect it up. If you size the pipes then you will see that if you have a combi and a cooker and a decent run 9/10 it will need some 28mm.
 
After all this, he phoned me this morning and said don't worry he is going to get the people moving the meter to make the connection. Suits me, i know he wouldn't have gone for a whole new gas run. I had it in mind to do what Steve has said. 28mm up to existing. (if sufficient)

Will be interesting to see what's there when i go back in a couple of days to pipe up some rads. It's all being buried, and they will want a combi in the future.
 
I can see why people over charge for work now. I was supposed to do this job Sunday (the rads and heating pipes, not the gas) He said he doesn't have the rad valve yet so can I come a different day or do it at night. I said yes, got a text today saying can't go tonight as he still doesn't have the valve. I told him I can do it wed and thurs night, if not it will have to wait until next week as I am booked up for the weekend. I doubt I will get to do the job now.
 
After all this, he phoned me this morning and said don't worry he is going to get the people moving the meter to make the connection. Suits me, i know he wouldn't have gone for a whole new gas run. I had it in mind to do what Steve has said. 28mm up to existing. (if sufficient)

Will be interesting to see what's there when i go back in a couple of days to pipe up some rads. It's all being buried, and they will want a combi in the future.

I had low pressure on a meter last week, provider came in and moved meter further away from the boiler. They piped it in 22mm, when I went back to check the wp at the boiler. It was wrong, they had to come back and re pipe it in 28mm. And this is the provider! Makes you wonder.
 
Status
Not open for further replies.

Similar plumbing topics

Yeah sorry, crappy powerpoint skills rather...
Replies
4
Views
3K
the Same position for meter but riser outside...
Replies
3
Views
2K
Looking at a meter installation like yours...
Replies
14
Views
5K
More than fine then in 11/5 tube should be...
Replies
3
Views
680
We've just sorted one of these situations...
Replies
9
Views
1K
Back
Top