Gas pressure problems, use of MDPE pipe outside? | Gas Engineers Forum | Page 2 | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Gas pressure problems, use of MDPE pipe outside? in the Gas Engineers Forum area at Plumbers Forums

Status
Not open for further replies.
Must be a huge bungalow to require a 37kw boiler.

and an incredible amount of bonding required

there is no way that a bungalow unless greater than 8 bedrooms (even then?) would require 37kw for heating so it must be for hot water, begs the question why not fit unveneted?
 
Last edited by a moderator:
I am looking at the gas supply, a huge run of 22mm to feed a gas thirsty 37kw boiler. Never stood a chance, I have seen 30KW boilers drop 3mb working pressure with 6m of 28mm in a 20m run.
Problem is this is a huge problem in our trade but many engineers dont have a clue how to check working pressures and gas rates etc, and many more cannot be bothered.
I have done a lot of inspecting and auditing in my time and half the boilers out there have more than 1mb drop in working pressure.
 
i have spoke to people who think there should be a 1mb drop, not that it is the max permissable!!!!!!!!

to be fair, in many cases you get away with it, if working pressure 23mb at meter and burner pressure needs to be 18mb you can get away with 5mb drop

i know the incoming could drop and it shouldnt be allowed but tis one of the reasons many ignore it
 
You wont get away with it at any of my local councils nor on Warmfront scheme, if its got more than 1mb drop then you upgrade the gas.
 
how many inspectors check your pressure drop across a system and on how many installations? you said people wont get away with it, but they do
 
What I meant was fitters dont get away with it on any contracts I am on, we have every job inspected by our own company and then by the initial company themselves.
But the difference is our work is surveyed properly in the first place, if you know what problems wil arise then you can rectify before it does, hence 28mm pipe on most of our jobs.
Its that initial survey that counts a lot I reckon, if you have the parts there and the knowledge that your work is gonna be checked twice, then believe me you do a good job and make sure its to ALL reg's.
I used to subby to a company doing all there surveys and inspections, I saw at least a dozen teams sacked in 12 months, I would put down x amount of 28mm gas due to boiler, pipe run and other appliances. Only to find that on the inspection after the work had been completed there was a 3mb drop on working pressure and no 28mm fitted, it had all been scrapped. Fitters reckoned it didnt need it when I asked so they were made to go back buy the 28mm themselves, fit it in there own time and when it was done, sack them. Poor workmanship is only going to lead to loosing contracts.
 
You wont get away with it at any of my local councils nor on Warmfront scheme, if its got more than 1mb drop then you upgrade the gas.

If you had seen the warmfront install at my mothers house then more than a 1mb drop would be the least of my concerns. The fact i had to repipe 75% of the heating system, the condense, blow off, re make 50% of the rad tails with enough ptfe, alter flue gradient......... infact it would be easier to list the things that was done correctly..... cant think of any thing! :( LOL
 
What I meant was fitters dont get away with it on any contracts I am on, we have every job inspected by our own company and then by the initial company themselves.
But the difference is our work is surveyed properly in the first place, if you know what problems wil arise then you can rectify before it does, hence 28mm pipe on most of our jobs.
Its that initial survey that counts a lot I reckon, if you have the parts there and the knowledge that your work is gonna be checked twice, then believe me you do a good job and make sure its to ALL reg's.
I used to subby to a company doing all there surveys and inspections, I saw at least a dozen teams sacked in 12 months, I would put down x amount of 28mm gas due to boiler, pipe run and other appliances. Only to find that on the inspection after the work had been completed there was a 3mb drop on working pressure and no 28mm fitted, it had all been scrapped. Fitters reckoned it didnt need it when I asked so they were made to go back buy the 28mm themselves, fit it in there own time and when it was done, sack them. Poor workmanship is only going to lead to loosing contracts.

done much installing yourself? your talking about sacking decent men here, who ve went back to put things right and then you sacked them? you could end up with a sore face treating men like that. you would if you tried that up here anyway.
Any idea how much the fitters are getting per system ?
just had an agency send me the prices they re offering for contract work with a national utility co. (not BG)
additional pipe - £7/3m copper LOL , thats alright if you ve got miles of straight runs , but when your working in occupied houses, moving furniture,lifting carpets, floorboards, checking joists, forming crossovers cutting in tees, tieing in existing branches, you can see where i m going here, £7 a length is taking the hit or a miss
pay fitters decent money, instead of peanuts, and the quality of the work will rise.

there s 4 man squads doing full systems in a day up here,up to 10 rads all copper, 15mm to rads, combi, gas upgrade. 2 fitters , a joiner , and a labourer . they re getting £450 a system , £150 ea fitter, £100 joiner and £50 labourer . sounds allright but its head down , backside up from 7.30 in morn till 7,8 or 9 at night, with up to an hour and half travelling each way. fitters are knocking their pans in for a £10 an hour , can see whythe gas upgrade gets swerved and the buckshee copper yadded :) , the squads don t get the scrap cylinders , fat cats even want that now.
 
It would appear you are suggesting I shouldn't have had a 37kW boiler fitted? The gas pressure problem was always a possibility and now its here a solution is sought. I am not Gas Safe Registered and do not intend to touch or alter any gas connections and will employ a gas safe registered person to do this (preferably the plumber who installed the boiler). However, I would like to explore the options with open minded experts before committing to one solution or another and discuss the relative technical constraints. I thought that was the purpose of forums such as this?

By the way, how many copper pipes have you left exposed outside that are connected to internal house bonding on a PME service? I don't want you to worry about it and I'm quite happy to share my concerns without fear of prosecution.

Couldn't agree with you more Brian99, this is a forum and raising questions are what they are all about (to me atleast.) Sadly there are alot of sad insecure people on this forum who wish to instantly jump down your throat.
However I would be concerned by who installed your boiler, If upsizing to a 37kw boiler. As a GSR installer the first thought you would have is pipe sizing! Although PE pipe-work is possible, would it not be easier/quicker to re-route internally and up-size. Any good GSR fitter/installer could do some calcs based on distance, fittings and output. Factory sheathed copper pipe is permitted buried in soil as is steel pipe, PE pipe and trac pipe providing they are buried atleast 375mm deep. Whatever happens there will be disruption.
Good Luck.
 
talking to a worcester engineer a while back, they re happy with min 14.5 WP on a Greenstar CDi (gas valve test point) as long as GR is within tolerances, any lower and they ll shut if off. something about the effect off the fan pulling the gas through. WP aint as important as a conventional boiler that need positive pressure to push the gas through.

worked on council sites where they ve pulled up fitters for flue terminals that are 295 from an opening, made firms take out 3/4" tracpipe and replace with 1" even though there was only 2-2.5 drop and GR was spot on. no other gas appliances in the properties. school boy errors by the fitter but a bit over the top imo even for new builds.

refurbs and grant aided jobs in occupied house are a bit different. knowing the theory and having a gas safe card and clipboard is cool but you can t buy practical experience.
 
done much installing yourself? your talking about sacking decent men here, who ve went back to put things right and then you sacked them? you could end up with a sore face treating men like that. you would if you tried that up here anyway.
Any idea how much the fitters are getting per system ?
just had an agency send me the prices they re offering for contract work with a national utility co. (not BG)
additional pipe - £7/3m copper LOL , thats alright if you ve got miles of straight runs , but when your working in occupied houses, moving furniture,lifting carpets, floorboards, checking joists, forming crossovers cutting in tees, tieing in existing branches, you can see where i m going here, £7 a length is taking the hit or a miss
pay fitters decent money, instead of peanuts, and the quality of the work will rise.

there s 4 man squads doing full systems in a day up here,up to 10 rads all copper, 15mm to rads, combi, gas upgrade. 2 fitters , a joiner , and a labourer . they re getting £450 a system , £150 ea fitter, £100 joiner and £50 labourer . sounds allright but its head down , backside up from 7.30 in morn till 7,8 or 9 at night, with up to an hour and half travelling each way. fitters are knocking their pans in for a £10 an hour , can see whythe gas upgrade gets swerved and the buckshee copper yadded :) , the squads don t get the scrap cylinders , fat cats even want that now.

I dont sack them, I was only inspecting there work. But the problem is, if they are leaving these problems and blatantly taking the mickey out of the company by tatting the copper in they have been given to upgrade the gas. I dont think the company are doing any wrong, and they aint good fitters if they are not doing there jobs right are they??
Not working to Gas Regs etc, this means companies lose contarcts, multi million contracts for some too.
If it takes 4 men do a 10 rad system in a day then no wonder they are struggling to make it pay. Most on our contarct are 2 men teams and all do 4 installs a week at least.
But not being nasty here, if a company knows they have good fitters then they pay a bit more, anybody can pay peanuts and get monkeys working for them can't they??
Oh and to answer your first question, I have over 15 years Gas exp mainly Heating installs and 20 years plumbing exp. I have done inspecting and surveying jobs in between and bits of auditing too.
 
talking to a worcester engineer a while back, they re happy with min 14.5 WP on a Greenstar CDi (gas valve test point) as long as GR is within tolerances, any lower and they ll shut if off. something about the effect off the fan pulling the gas through. WP aint as important as a conventional boiler that need positive pressure to push the gas through.

worked on council sites where they ve pulled up fitters for flue terminals that are 295 from an opening, made firms take out 3/4" tracpipe and replace with 1" even though there was only 2-2.5 drop and GR was spot on. no other gas appliances in the properties. school boy errors by the fitter but a bit over the top imo even for new builds.

refurbs and grant aided jobs in occupied house are a bit different. knowing the theory and having a gas safe card and clipboard is cool but you can t buy practical experience.


But why do a job thats not to reg's?
295mm is not to reg's and yes its only 5mm but its not right.
2.5mb drop is not allowed, it says 1mb for a reason and Worcester and other companies are handing out leaflets to companies about working pressure drops, they are allowing a bit more now due to gas valves. Think Worcester allow 1mb extra so you are allowed 2mb on them.
But you try telling that to an inspector who only knows the 1mb drop rule.
If you are gonna bend the rules a bit, do it where it aint gonna matter or be seen. Cause the first thing you check is the flue.
 
not sure 5mm is going to make a difference wether pocs from a fan flue enter a building or not, obviously the further away the better. if they re going to enter at 295mm, why wont they enter at 300mm or 305mm. i thought gas regs were there for safety and guidance for engineers, not to give mini hitler jobsworth inspectors a cushy job and power trip.
i know and work to the regs . 2.5mb drop is allowed, and classed as ncs if not affecting safe operation of an appliance.
you must be installing a lot of 35mm copper if your sizing correctly to houses with multi gas appliances and high output combis then.
i explain this to customers who dont want their expensive flooring ripped up to upgrade a gas supply when the new boiler will operate perfectly well and safely with correct GR , on the existing 22mm supply.
 
few weeks since last fitted 1 but sure worcester CDi combi MIs state a WP of 16.5 is ok allowing for drop accross the gas valve, their engineers were informed anything less than 14.5 they have to ar.
BG 330 MIs state 15 minimum , if i mind right. i go with MIs .
 
few weeks since last fitted 1 but sure worcester CDi combi MIs state a WP of 16.5 is ok allowing for drop accross the gas valve, their engineers were informed anything less than 14.5 they have to ar.
BG 330 MIs state 15 minimum , if i mind right. i go with MIs .

WB cdi min 18mb in instructions which includes any drop across the gas valve. any install that has more than a 1mb drop is incorrect as per gas regulations, it dont matter what the min value the boiler needs to run correctly. If you have more than a 1mb drop then its wrong, simple.

MI state the min requirements of the applaince, this does not alter the need to correctly size the gas pipework to avoid a drop of more than 1mb.
 
not sure 5mm is going to make a difference wether pocs from a fan flue enter a building or not, obviously the further away the better. if they re going to enter at 295mm, why wont they enter at 300mm or 305mm. i thought gas regs were there for safety and guidance for engineers, not to give mini hitler jobsworth inspectors a cushy job and power trip.
i know and work to the regs . 2.5mb drop is allowed, and classed as ncs if not affecting safe operation of an appliance.
you must be installing a lot of 35mm copper if your sizing correctly to houses with multi gas appliances and high output combis then.
i explain this to customers who dont want their expensive flooring ripped up to upgrade a gas supply when the new boiler will operate perfectly well and safely with correct GR , on the existing 22mm supply.

2.5mb drop on a new install is not NCS.

cost of materials or flooring is not a vaild excuse to break the regs.
 
As for 1 day installs, i have yet to see one installed correctly and to the book. if you consider you need atleast 4 hours to commission correctly (cold flush, hot flush after min 2hours, balance etc...) thats why so many engineers have loads of bottles of cleaner on the back of the van. lol
 
we all know the regs state 1mbar drop between meter and appliance. it's outdated though.
if i can prove a premix burner is working to full performance with correct GR/HI , temp rise on DHW, CA values, no affect on safety of any other appliances, as a gas engineer i m happy as larry. if it s not performing to full performance and is undergassed , then it gets upgraded . thats engineering judgement , and no reg is going to tell me a boiler operating perfectly on a 22mm supply is going to work better on a 28mm

suppose yous all always calculate the IV of the pipework for purging as well lol

tamz knows the script , watch out for a TB on coming soon
 
Status
Not open for further replies.

Similar plumbing topics

More than fine then in 11/5 tube should be...
Replies
3
Views
685
H
My gas kiln is similar (different british...
Replies
6
Views
3K
Hotwork40
H
Well if you are getting the gas meter moved to...
Replies
5
Views
3K
I have connected the secondary pump to a wifi...
Replies
9
Views
2K
H
Hi there, thanks for your time to look at this...
Replies
0
Views
920
HRP123
H
Back
Top