Hi, I have stripped down my own boiler today as it had developed explosive ignition. I am thinking it is the ignition electrode as just below it on the burner is a black soot mark. So that has been ordered. I gave my kane 455 ago for the first time since buying it and it says the ratio 0.0002. But when I do a Gas rate it is under what the manufacturer states. I have cleaned the heat exchanger, burner and fan is ok. Inlet working pressure is fine and burner pressure is correct.

Not sure what else to do really?
 
Leave it alone maybe :)

Gas rating isn't an exact science in my experience mutley racer. By the time you've got to the meter and done your 2 mins the boilers modulating down!! :) What's the make and model?
 
its in ft3. Are the tolerences 5% lower and 10% higher when gas rating? Like on most new boilers
 
Like diamondgas says, gas rating isn't always accurate. I fitted a Halstead boiler recently (customer wanted cheap, cheap, cheap), out was a 1-bed flat, 4 rads, and a warm day. Couldn't get the boiler to stay on full burn for 2 minutes, even! No way of forcing full burn, no service mode, nada. Everything else was spot on, so that was that..
 
yea, no service mode on this either. The boiler seemed to be running all the time though as I could hear it. Also, I had a cold hot water cylinder to fill up and a heating system to warm
 
it says 57 in the book and I am burning 52

That's a good thing, Lower bills :)

Try an average over a period of time if your concerned. Obviously the gas rate is best done with the system cold on heating only to guarantee the boiler staying on max rate for the duration of timing. You could try timing over a longer period of time to give you a more acurate reading providing it stays on max throughout :) Did you get the temp clamps too Mutley R? Check out the diff F&R. I played about with mine when i first got it. Found out i have a 2mbar drop somewhere!! :D
 
Last edited by a moderator:
I actually have timed it on 4 different occasions. Still coming up the same every time.

Yep i have got the flow and return clamps. i shall give those ago? Not quite sure what you mean by a 2mb drop on them though?

Did you plug them into the wrong part on the analyser or something??
 
I actually have timed it on 4 different occasions. Still coming up the same every time.

Yep i have got the flow and return clamps. i shall give those ago? Not quite sure what you mean by a 2mb drop on them though?

Did you plug them into the wrong part on the analyser or something??


LOL .... No I did the let-by and tightness test! Got a gas leak somewhere!! lol

Regards the gas rate though, what would you do to rectify the issue. By the way it may be worth checking the operation of the gas valve! Checking the p2 operation pressure :)
 
The 15 HE?
Is that not a standard gas valved boiler with burner pressure adjustment?

Ignore the above. Been a long day. Not long in.
 
Last edited:
the burner pressure is correct, 9mb. A leak hey, thats funny. You're allowed a 4mb drop or 8mb though hey. Am not sure how to fix it Diamond, that is why I am talking to you guys with lots of experience. I have only been on my own for 2 months
 
Burner pressure spot on.
FGA readings are good.
Your Gas Rate is within 10% (measurement error. you will very rarely get it spot on)

If the above is correct you have nothing to worry about.
 
Soz mutley for some reason I thought it was a zero compensating governor .. got the mi's now and it all becomes a lot clearer regard the boiler in question :)

You don't have a problem as such, by the way! However if everything is correct yet the gas rate is less than expected what would you check? rather than give you the answer I'd like to stretch you a bit if you don't mind :)

Hold on this is probably best in the gas safe only forum... puddle!!!! :)
 
10% either way is it GrahamM? For some reason I thought it was 5%below or 10% above. If you are right then it is just perfik. Thanks guys

I am a happy chappy now
 
I am really trying to get into the Gas safe only forum but am not getting a reply from dan. He is really busy apparently. I thought it could be a blocked burner, injector. Undersized pipe. But all of them are fine
 
Can puddle let me into the gas safe only part if i pm him my details? Also, Burner pressure is spot on
 
10% either way is it GrahamM? For some reason I thought it was 5%below or 10% above. If you are right then it is just perfik. Thanks guys

I am a happy chappy now

5% above and 10% below. recent gas safe tech bulletin about it.

even more of a pain when you are gas rating on those meters that you keep having to press the button for a reading.
 
Last edited:
Doing a gas rate is not an exact science as mentioned. Too many variable affecting a correct answer.

There is an un-written rule that most engineers use to compensate for the measurement error which is inevitable. This is usually 10% bellow and 5% above the MI's.
 
I am really trying to get into the Gas safe only forum but am not getting a reply from dan. He is really busy apparently. I thought it could be a blocked burner, injector. Undersized pipe. But all of them are fine

Me too! I guess they're pretty busy, just have to be patient! :)
 
I am really trying to get into the Gas safe only forum but am not getting a reply from dan. He is really busy apparently. I thought it could be a blocked burner, injector. Undersized pipe. But all of them are fine

Strange !!! Dan's normaly on the ball, Not sure if Super Mod can authorize your acceptance to GSR only mate :) You got it about right though .. issue would lie down stream of the gas valve within the appliance .. most likely suspect would be injector ... however in the old days they use to say check 'hot' which may make a bit of a difference as the injector expands? :)
 
Last edited by a moderator:
shame masood, How long have you been waiting? Me over a week now.

Oh, so I had it the wrong way around. So all is fine. Thanks chaps.

Incidentally the things I mentioned Diamond are ok?
 
Status
Not open for further replies.

Similar plumbing topics

More than fine then in 11/5 tube should be...
Replies
3
Views
679
Set whatever boiler you're installing to the...
Replies
2
Views
917
If you have the right temperature rise for the...
Replies
10
Views
3K
Conditions: nearly 10 year old boiler WB2B...
Replies
0
Views
600
Thanks some good ideas. Just as an aside if we...
Replies
10
Views
2K
Back
Top