The calculations will vary region to region according to the calorific value of the gas. Unless you know and use that in your calcs you are working to an approximation.
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Discuss Gas rate app in the Gas Engineers Forum area at Plumbers Forums
The calculations will vary region to region according to the calorific value of the gas. Unless you know and use that in your calcs you are working to an approximation.
No mention of checking the cv of the gas in any text book or reg I have seen. The difference is probably that minimal it has no affect.
Up to 5%
Sent from my GT-I9100 using Tapatalk 2
Well if BG say so then I'm ditching mine :willy_nilly:
Be better teaching some of the lads the back boilers need ventilation!
I'm saying I regularly go to CF installs with no ventilation that used to be under a BG contract since installation but they can't afford it, when I tell them what needs doing I normally get asked to leave because "British Gas never mentioned that".Are you suggesting British Gas engineers work unsafely?
Sent from my iPad using Tapatalk HD
I'm saying I regularly go to CF installs with no ventilation that used to be under a BG contract since installation but they can't afford it, when I tell them what needs doing I normally get asked to leave because "British Gas never mentioned that".
I can only speak from e pertinence and I wish I had a pound for every time it's happened.
Exactly! As I touched on previously. :wink_smile:BG wanting to ban the use of apps is not because they are wrong. They are not. They will just want to standardise their info they receive back by having there guys use the same method.
Btw i had a job last year where the incoming pressure was below 10mb (water in the service) and the boiler gas rated and was running perfect! Work that one out¿¿¿
In reality the cv of the gas doesn't really affect your calculations as all you are checking is that the boiler is passing the correct amount of gas.
Injectors are sized to pass a certain amount of gas at a certain pressure and zpg's set to draw the correct amount of gas nearly no matter what the inlet pressure is (unless it is very low). That is (should be) the constant you are checking against what the manu says it should work out at.
You have no way of knowing the actual HI of the boiler as that is the variable (due to the cv).
It just means if you live somewhere with a high cv your combi will give a bit better hot water and if you live in London your onto plumbs as your cv is generally lower :lol:
Btw i had a job last year where the incoming pressure was below 10mb (water in the service) and the boiler gas rated and was running perfect! Work that one out¿¿¿
In reality the cv of the gas doesn't really affect your calculations as all you are checking is that the boiler is passing the correct amount of gas.
Injectors are sized to pass a certain amount of gas at a certain pressure and zpg's set to draw the correct amount of gas nearly no matter what the inlet pressure is (unless it is very low). That is (should be) the constant you are checking against what the manu says it should work out at.
You have no way of knowing the actual HI of the boiler as that is the variable (due to the cv).
It just means if you live somewhere with a high cv your combi will give a bit better hot water and if you live in London your onto plumbs as your cv is generally lower :lol:
Btw i had a job last year where the incoming pressure was below 10mb (water in the service) and the boiler gas rated and was running perfect! Work that one out¿¿¿
Maybe he rated it before he found the water?Why would you gas rate a boiler which has 10mb incoming pressure and water in the service.
Sent from my iPad using Tapatalk HD
Why would you gas rate a boiler which has 10mb incoming pressure and water in the service.
Because i'd just fitted it and was commissioning it of course.
Guage on the boiler and fired it up. Dropped down to below 10 straight away. Guage on the meter (3 ft away), bouncing between about 8 and 12mb. I rated it out of curiosity. It was perfect.
Boiler was a 30si.
Water gets into the mains sometimes up here and can work itself into the service. If you disconnect the ecv you can hear it gurgling and sometimes you can get some out.
SGN cut the pipe in the street and blew it with the compressor.