my teacher told us u dont need to know all the regs by head, but u should know where to find them


see techers do know what they are talking about, very good advice you got, very few people will be able to learn all the regs, but the trick is to learn all the basic things you need to do every day and know where to find the rest
 
Sorry to Hijack.

Garry38, I reckon i know you, same college up here in Scotland, lets not mention it just yet. Our lecturer in the college was an absolute nightmare, and still at his same old tricks leading students up the garden path, saying NVQ2,3 is very easy to complete, when in fact there was plenty to organise and keep evidence for.

Im in the process of gaining gas experience to qualify for ACS, which i hope to take in the summer.

Looks like a decent forum guys, keep up the good work.

Al
 
had gas safe visit there really was straight forward they were not out to catch me out and really helpful...
was really dreading it before but as i no all checks etc to carry out and everything i need to no it went realy well. :D

Sorry to Hijack.

Garry38, I reckon i know you, same college up here in Scotland, lets not mention it just yet. Our lecturer in the college was an absolute nightmare, and still at his same old tricks leading students up the garden path, saying NVQ2,3 is very easy to complete, when in fact there was plenty to organise and keep evidence for.

Im in the process of gaining gas experience to qualify for ACS, which i hope to take in the summer.

Looks like a decent forum guys, keep up the good work.

Al

send me private message to see if i no you....
 
Last edited by a moderator:
Garry, I cant sent private message as you need minimum of 5 posts :mad:.

Im glad your visit went well with you inspector, fantastic news. ;).

Take a look at the username Garry, the clue is in there.

I'll text you later if you cant guess.

Al
 
A bit worried now!!! My gas part supplier informs me that I need a gas annalyser for the gas inspection !!!
I can't see why?
It is not a regulation (yet) and I use flame picture and gas rates to determine safety of appliances anyway.
Can anyone clarify this???????
Rob
 
if you had a test point before the boiler isolation valve you would be seeing at least 21mb loss is through the isolation valve internal pipework and multifunction valve if you ask the manufacturers what the resistance is through these itemsthey should be able to tell you i think worcesters qouted 1 mb
Steve Is correct, worcester Bosch has a technical bullet in about it, on a Vaillant you can lose as much as 2.5mbar across the isolator even with a short run of 28mm!
 
iv got my inspection in a few days reading these threads have really made me feel more at ease. cheers lads
 
A bit worried now!!! My gas part supplier informs me that I need a gas annalyser for the gas inspection !!!
I can't see why?
It is not a regulation (yet) and I use flame picture and gas rates to determine safety of appliances anyway.
Can anyone clarify this???????
Rob

Does the commissioning of the boiler require you to have an analyser? e.g. on Remeha boilers you have to check and set the CO & O2 levels!

Saying that - I had an inspection a few weeks ago, even though I have CPA1, I got the impression that as long as the gas rate is ok they don't see it as mandatory the have an analyser.

The inspectors are not too bad, I'm sure you'll be fine
 
Last edited by a moderator:
Status
Not open for further replies.

Similar plumbing topics

If you can afford to lose 1/2 or more of your...
Replies
7
Views
2K
I
No your fine just make sure there registered...
Replies
1
Views
1K
Morning All. We have a gas safe inspection...
Replies
0
Views
1K
Id say recal at that price....as soon as it...
Replies
5
Views
961
Back
Top