Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss glowworm compact 60 system boiler in the Boilers area at Plumbers Forums

Status
Not open for further replies.
T

tomkelly

Hi all a little advice please.I changed a fan that was knackered and the boiler only fires and runs for about 1 min. gas goes out then relights and runs for 1 min..... if I loosen the casing it will stay running, I was wondering if the new fan may be at fault as the flue is clear gas to boiler is fine ect. I would be greatful for any advice as Im new to boiler repair been fitting them for years.
 
sounds like aps, flue or venruri fault, are you sure you put the hoses to the aps/venturi the correct way around? may be worth swaping over to see if that makes any diffrence, also check venturi is clear and that you didn't dammage it while replacing fan
 
As said make sure tubes to fan are not damaged and correct way round and that you put a new gasket between fan and housing

imho
 
OUCH I hope you installed something with a 5 year guaranteeeeeeeeeeeeeeeeeeeee
 
Status
Not open for further replies.

Similar plumbing topics

Thanks Enthalpy, Your conclusion is exactly...
Replies
12
Views
2K
Who said plastic 28/22mm copper tube and mlcp...
Replies
3
Views
802
Finally (I hope) got to the bottom of this...
2 3
Replies
55
Views
5K
I
Yes press the button until there are 2 lights...
2 3
Replies
53
Views
6K
Deleted member 120897
D
The Orion is about 65% efficient so not great...
Replies
10
Views
3K
Back
Top