Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Grant Vortex Combi 21e no central heating in the Central Heating Forum area at Plumbers Forums

Messages
4
Hi,

I've recently put some heating/hot water pipes into the floor as there were exposed previously. On refit of the pipes i've gone to test the boiler functionality however, the central heating won't fire.

The hot water works perfectly.

There is no CH light on the boiler and the return pipe warms up slightly however, there is no hot water on the supply side and the pump doesn't run. If i've accidentally switched the pipes over would this cause this issue?

Thanks for any help,

Chris
 
If theres no central heating demand light then it's not getting a signal to run central heating.
If theres no central heating demand light then it's not getting a signal to run central heating.
Hi Simon,

I've just wired in a brand new thermostat and four new wires directly into the boiler to test if there's a fault with the thermostat/wiring. The fault still remains.

Is there another way of testing whether the boiler is getting a signal to run the central heating?

Thanks
 
If you have a multimeter and are competent to use it check if you have a live feed on 6 (heating pump )
If your boiler is feed by a 5 pin plug check you actually have a live feed on heating feed.
It is known for circuit board to fail on heating side particularly if water has somehow got in (not enough care when venting heating pump usually)
 
Last edited:
Hi.....I experienced same issue.........I called out the Grant engineer who explained to me,.......
The Grant Combi oil boiler is hot water priority......when the boiler starts, it will run with hot water only, until the hot water supply is up to temperature. Then the heating kicks in.
So wait and iot will work, after 5 minutes or so.
 

Similar plumbing topics

Sometimes the connection point of the cylinder...