Gravity hot water to fully pumped / sealed | Central Heating Forum | Plumbers Forums
Guest viewing is limited

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Gravity hot water to fully pumped / sealed in the Central Heating Forum area at Plumbers Forums

Messages
149
One of our installers currently fitted a new heat only boiler to replace an old floor standing with gravity hot water. At the time he never fitted any valves or cylinder stat etc so I have been called back there to basically start again. Been there today to do it and found that he had the pump on the return. Anyway I drained system and made the necessary alterations to the pipework by the boiler and fitted a mid position valve and a wireless cylinder stat (as the run is impossible to get a cable between the two). So currently the feed from the F + E tank goes into the return of the cylinder and the vent on the flow. The boiler is in a tight cupboard low to the ground in an extension of the side of the house and the cylinder is on the 1st floor in the middle of the main part of the house so you can imagine how the pipework runs
 

Attachments

  • 20200103_194007.jpg
    20200103_194007.jpg
    120.9 KB · Views: 63
  • 20200103_194001.jpg
    20200103_194001.jpg
    119 KB · Views: 58
Crikey that looks snug! The filter is gonna be a devil of a job to open up!
Yeah very tight. The filter is tight but can be open now. I've attached a pic of what it looked like before. Our surveyor has really mucked up here to be honest. He should of quoted for a system boiler for a start.
 

Attachments

  • dbo_60711844-62e0-41c1-9bb4-b3ef51d85aaa.jpg
    dbo_60711844-62e0-41c1-9bb4-b3ef51d85aaa.jpg
    57.7 KB · Views: 48
  • dbo_e912cbe5-decc-420f-b082-db91ed36d03a.jpg
    dbo_e912cbe5-decc-420f-b082-db91ed36d03a.jpg
    70.5 KB · Views: 46
So this is an open vented system and not sealed? Pump can go on return on a vented but the cold feed should be piped to down into return shortly after the pump outlet, the system would be under negative pressure though. To be honest that looked a mess beforehand
 
So this is an open vented system and not sealed? Pump can go on return on a vented but the cold feed should be piped to down into return shortly after the pump outlet, the system would be under negative pressure though. To be honest that looked a mess beforehand
yes, open vented at the moment. Problem is that I cant make any alterations to the feed & vent on the cylinder as its as tight as a .......... and there is no way i can get feed or vent down to pump / boiler position. Bloody nightmare of a job.

Do you think my idea will work ok ?
 
agree pump should be on the return as they tend to last longer due to lower temp

check valve on the feed from the f and e
and a 2 bar safety valve on the vent
expansion vessel

thats along as you have an okish head eg 3m+

 

Attachments

  • 1.JPG
    1.JPG
    102.3 KB · Views: 53
Last edited:
agree pump should be on the return as they tend to last longer due to lower temp

check valve on the feed from the f and e
and a 2 bar safety valve on the vent
expansion vessel

thats along as you have an okish head eg 3m+

So are you saying still use the F + E tank to fill the system and fit a check valve to the feed, 2 bar PRV on the vent as well as an expansion vessel or am i doing away with the f + e and filling via mains water ?

Also gonna have to leave the pump on the flow now as ive already changed it all now. Will that matter ?

Only place I can get vessel in is either above the boiler on the ground floor or in the place of the f + e tank.
 
If you leave the vent as is then whenever HW is called for it will pump over, in time it will sludge up the system. Im assuming Shaun is suggesting seal the system and do away with f and e tank, which is what I would suggest. Preferably the expansion vessel will go on return where it’s not exposed to high temperatures, if the pump is on return the vessel should be close to suction inlet of pump to maintain a positive pressure through boiler and around the system, thus eliminating any air ingress.
 
So are you saying still use the F + E tank to fill the system and fit a check valve to the feed, 2 bar PRV on the vent as well as an expansion vessel or am i doing away with the f + e and filling via mains water ?

Also gonna have to leave the pump on the flow now as ive already changed it all now. Will that matter ?

Only place I can get vessel in is either above the boiler on the ground floor or in the place of the f + e tank.

leave the f and e tank in so it will stay the same pressure

sealing could cause issues with leaking on joints etc if in a concrete floor
 
If you leave the vent as is then whenever HW is called for it will pump over, in time it will sludge up the system. Im assuming Shaun is suggesting seal the system and do away with f and e tank, which is what I would suggest. Preferably the expansion vessel will go on return where it’s not exposed to high temperatures, if the pump is on return the vessel should be close to suction inlet of pump to maintain a positive pressure through boiler and around the system, thus eliminating any air ingress.
Thats what I thought. Think I will fit the vessel above the boiler on the return, remove the f + e tank and fit AAV's on what used to be the feed and vent. At least this way the coil can release trapped air
[automerge]1578097374[/automerge]
leave the f and e tank in so it will stay the same pressure

sealing could cause issues with leaking on joints etc if in a concrete floor
[automerge]1578097473[/automerge]
leave the f and e tank in so it will stay the same pressure

sealing could cause issues with leaking on joints etc if in a concrete floor
Would love to but cant see how im goona get over the airlock issue. This way I can fit AAV's on the old feed and vent pipe once i remove the tank
 
But the vent is on flow of HW, not only will this pump over when calling for HW but the vent is not open if valve is shut?

will have a 2 bar blow off on the end of it so no pumping over
[automerge]1578098152[/automerge]
Air lock issue ??
 
I’ve done one to date couldn’t seal due to pipework and not enough pressure

worked ok and no complaints so far been in 2 years
 
In case of any worries re pressurising the system (old pipework etc) it might be no harm adding that the E.vessel should have its pre pressure reduced to whatever the static head is and be as large as comfortably possible , that way the final pressure will still be very very low, probably < 1 bar with hot system.
 
I agree with John to a degree. The expansion vessel pre charge should be set higher than the static head at that point. The system should be then be pressurised to roughly .2 bar higher. Yes a larger expansion vessel is not a problem but one you're tight for space and two theres no point spending additional money on a 50 litre if a 12 is enough. You need to calculate the vessel volume required using system volume etc. Like I said ideally you want the vessel on the return, tapped in just before pump inlet, this will give the neutral point at that tap in, negative pressure in short piece of pipe before pump and then positive pressure through boiler and rest of system back to neutral point, thus eliminating possibility of air ingress.
 
I wouldn't like to see the EV pre pressure < 0.4 bar in case it doesn't push the diaphragm up against the opposite end, and because you will always have "auto filling" via the F&E tank then there is no need for a EV water reserve so Pre & filling pressure in these systems can be the same IMO, assuming system volume of 100 litres and a mean boiler temperature of 75C and assuming a static head of 4M with a 12 litre EV then the maximum system pressure will still only be 0.76 bar when hot. If one "forgot" to reduce the pre pressure then 1.0 pre pressure will result in a final pressure of 1.52 bar and 1.5 pre pressure will result in a final pressure of 2.15 bar.
Bord Gais approved RGIs here have installed literally "tens" of these systems near me on converting from oil to gas with no problems whatsoever, they use(d) swing check NR valves (which have to be installed in the horizonal) rather than the poppet type.
 
John where are you getting this info to calculate the vessel charge and system pressure when hot? It seems to be more in depth than what I have in front of me, can you supply a link?
 
I just work(ed) it out from first principles many years ago when I was involved in industrial pressure vessels, boilers etc, you (or anyone) can input your own numbers here.
 

Attachments

  • Expansion Vessel Calculation Extract Rev 3.zip
    9.9 KB · Views: 43
That's it, it was in lotus 123 originally before excel was even heard of!!
I have just added another "box" to give a taste of a fairly typical (fully sealed) installation, its quite handy.
 

Attachments

  • Expansion Vessel Calculation Extract Rev 4.zip
    10.2 KB · Views: 33

Similar plumbing topics

Everything working fine on PP mode - thanks...
Replies
7
Views
1K
Yes it will be controlled on boiler thermostat.
Replies
3
Views
621
Hello, I live in a two floor semi with a...
Replies
0
Views
818
G
Could be one of a number. Need to know what...
Replies
1
Views
689
see same. below on this as some one has had...
Replies
1
Views
910
Back
Top