Re Static Head, I didn't include this is because I don't know where the EV will be located, if its located just above the boiler on the ground floor then you would add ~ 0.1 bar to the final pressure to get the maximum (and ) boiler system pressure, more significantly, but a bit unusual, if the EV was located in the attic then you would add ~ 0.4/0.5 bar to the final (EV) pressure to arrive at the maximum (and ) boiler system pressure, if in the hot press then add - 0.25 bar, and so on, with EV mounted above boiler (ground floor) then the pre pressure should not be less than 0.4/0.5 bar to ensure that you will get circulation through the upstairs rads on boiler start up.
Re System Volume, again I didn't include it directly in the calcs BUT I give a table with the % expansion for water temps from 50C to 110C, so for example if you estimate that your system contents are 100 litres and that the flow/return temps are say 75C/60C, mean of 67.5C...from the table this equals ~ 2% expansion so total expansion is 100*2% or 2 litres which you insert in the yellow box adjacent to "expansion"
You can see the calculations in the excel S.Sheet if you highlight each cell.
Thanks John. I was overlooking thermal expansion coefficient on the left of boxes 🤦♂️
[automerge]1578166817[/automerge]
How would an expansion vessel under charged at ground floor level affect circulation in upstairs rads on start up @John.g?
might be best to start a new thread as im sure theres more people who would like to learn this information
Thanks John. I was overlooking thermal expansion coefficient on the left of boxes 🤦♂️
[automerge]1578166817[/automerge]
How would an expansion vessel under charged at ground floor level affect circulation in upstairs rads on start up @John.g?
Hi all just thought id update you with todays result. So i did what i thought was best and fitted and 18 ltr vessel above the boiler, took out the f + e tank and fitted AAV's on the feed and vent pipes from the cylinder coil. works an absolute treat.One of our installers currently fitted a new heat only boiler to replace an old floor standing with gravity hot water. At the time he never fitted any valves or cylinder stat etc so I have been called back there to basically start again. Been there today to do it and found that he had the pump on the return. Anyway I drained system and made the necessary alterations to the pipework by the boiler and fitted a mid position valve and a wireless cylinder stat (as the run is impossible to get a cable between the two). So currently the feed from the F + E tank goes into the return of the cylinder and the vent on the flow. The boiler is in a tight cupboard low to the ground in an extension of the side of the house and the cylinder is on the 1st floor in the middle of the main part of the house so you can imagine how the pipework runs
Hi all just thought id update you with todays result. So i did what i thought was best and fitted and 18 ltr vessel above the boiler, took out the f + e tank and fitted AAV's on the feed and vent pipes from the cylinder coil. works an absolute treat.
yes and the best way. do like your info on the other way though but why mess about with that when its just as easy to seal it isn't it ?So now, a fully sealed system.