The heat carrying capacity of copper pipe BS EN 1057 is
15mm = 10kW with a temperature drop of 11C and a velocity of 1.5m/s.
22mm = 22.14kW
It also varies with velocity the faster the more kW but usually 1.5m/s is the maximum and 0.3m/s the minimum.
But at 0.3m/s its
15mm = 2kW
22mm = 4.42kW
Quite a lot isn't it?
Google copper board "Copper in small bore central heating systems" it tells you there.
What use is it?
Well you get the heat output of your rad and it tells you what size pipe will suite.
So 3 - 5kW rads needs a 22mm supply, but you can reduce to 15mm after the first one as the other two only need 5kW each. In practice of course you have to take account of heat loss from the pipes as well.
But its a rough guesstimate rule of thumb way. Which being honest, if your motoring and people moaning at you, the stress is building, you ain't usually got much time for thinking things out in a leisurely way. So you want a quick way to do things.
Anybody add tips for the newbies?
15mm = 10kW with a temperature drop of 11C and a velocity of 1.5m/s.
22mm = 22.14kW
It also varies with velocity the faster the more kW but usually 1.5m/s is the maximum and 0.3m/s the minimum.
But at 0.3m/s its
15mm = 2kW
22mm = 4.42kW
Quite a lot isn't it?
Google copper board "Copper in small bore central heating systems" it tells you there.
What use is it?
Well you get the heat output of your rad and it tells you what size pipe will suite.
So 3 - 5kW rads needs a 22mm supply, but you can reduce to 15mm after the first one as the other two only need 5kW each. In practice of course you have to take account of heat loss from the pipes as well.
But its a rough guesstimate rule of thumb way. Which being honest, if your motoring and people moaning at you, the stress is building, you ain't usually got much time for thinking things out in a leisurely way. So you want a quick way to do things.
Anybody add tips for the newbies?