customer complaining regarding heating running on low heat around 40.c at most, showing on front panel.
Have push up tempreture to maximum of 65c but boiler just dosnt seem to go beyond 40.c.
Hot water works fine.
Its a small flat with 3 radiators 1 large and 2 medium size, have carried out system flush as water was very dirty but has not made much difference.
By removing actuator motor and turning hot water tap on, the heat will go on heating side perfectly reaching tempreture of 80.c and all rads are piping hot, which takes out any doubts about blockage.
Have also replace flow and return ntc's with no effect
The other trouble is there is no technical help with heatline as they seized to exist.
Any help would be much appreciated.