Went to a job today. Tenant complaining that the rads were getting hot when the room stat was off.
Y plan system fully pumped, old potterton heating only boiler.
On investigating I found that the programmer had been wired so it gave a permanent live to the room stat regardless if the heating was set to on, auto or off. BUT the room stat was functioning fine.
3 port was functioning fine, I.e was opening easily and was firing up the boiler when put in demand by the room stat. Got correct voltages from the white, orange and grey when in demand on heating only etc.
Took the face off the programmer and boiler was still firing up.
I think the programmer has been wired wrong personally but what else could or should I have checked?