Our HeatraeSadia Electromax boiler has just been serviced. Since the service we get a lot of vibration from the system each time the hot water is run after the system has been heated up. After some investigation and correspondence with the service engineer we concluded that it was probably
because the charge pressure in the expansion vessel was higher than the dynamic pressure of the cold water supply, which can lead to a short period of vibration as system pressures equalise when hot water is drawn off. He came back to lower the pressure in the EV ( taking 0.5 bar of it ) and he measured the supply pressure ( which he said was reasonable, but I don't have the actually measurement ). Since then the vibration has been better but it is still there. Do you think we are on the correct path to fix the issue, or is there something else that could be causing this problem. The service engineer tried to convince me that by bringing the EV pressure back to the correct level in the service it might have uncovered another issue ( which would need further investigation and by implication more cost ). Any advice gratefully received.
because the charge pressure in the expansion vessel was higher than the dynamic pressure of the cold water supply, which can lead to a short period of vibration as system pressures equalise when hot water is drawn off. He came back to lower the pressure in the EV ( taking 0.5 bar of it ) and he measured the supply pressure ( which he said was reasonable, but I don't have the actually measurement ). Since then the vibration has been better but it is still there. Do you think we are on the correct path to fix the issue, or is there something else that could be causing this problem. The service engineer tried to convince me that by bringing the EV pressure back to the correct level in the service it might have uncovered another issue ( which would need further investigation and by implication more cost ). Any advice gratefully received.