Help-Central heating probs? | Central Heating Forum | Page 2 | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Help-Central heating probs? in the Central Heating Forum area at Plumbers Forums

Status
Not open for further replies.
Although rereading that it looks more like a balancing issue!

How To Balance Radiators
Tool List:

Radiator-bleeding key
Lockshield valve adjuster or adjustable spanner
Screwdriver
Digital thermometer or multimeter with thermometer function



1. Make sure all the radiators have been bled. Turn off the central heating and allow the radiators to cool.

2. Familiarise yourself with the valves. The lockshield will usually have a push-on cap or one that is secured with a screw through the top. Remove it.

3. Older models will have a wheelhead valve on the other side — used to turn the radiator on/off.

4. Newer radiators will have a thermostatic valve instead of a wheelhead valve.

5. Open up the valves on all the radiators in the house by turning them anti-clockwise.Wheelhead and thermostatic valves can be turned easily by hand, but the lockshield will need a plastic adjuster to open it up. These come with new lockshield valves. A spanner will also do the job.

6. Turn the central heating back on and note down the order the radiators heat up. Those nearest the boiler normally get hot first. If you’ve got a lot of radiators, get assistance. Turn the heating off and wait while the radiators cool down.

7. When the radiators are cool, switch the heating back on and go to the first radiator on your list. Turn the lockshield valve clockwise until it is closed and then open it by a quarter of a turn. Once the radiator has warmed up, take a temperature reading at the pipework leading to one of the valves.

8. Now take a temperature reading at the pipework leading to the other valve and open the lockshield valve gradually until there’s a 12°C difference between now and the reading you took in step 7 (allow a couple of minutes after each adjustment for the temperature to change). The temperature figures indicated in the last step and this one are relevant to the radiator shown – don’t take them as any kind of optimum figure – it’s the 12°C difference in temperature at the valves that counts. Next, check the rest of the radiators in the system following the order in the list. The further you move away from the boiler, you’ll find the lockshield valve will have to be opened more. The last radiator may need to have the lockshield valve fully open to work at full efficiency. Your radiators are now balanced and should work perfectly.

Getting A Temperature

A key part of this job is measuring the temperature difference across each radiator. Specially designed thermometers that strap round the pipes at either end of the radiator are available to buy or hire, but it’s not really necessary to use these. You can get away with a single digital thermometer — it just means that you can’t take simultaneous readings and you’ll have to move from one end of the radiator to the other.

Digital thermometers are available from around £10. Alternatively, some digital multimeters have a temperature sensor function. A digital multimeter with temperature function costs from £25 and can also be used for taking electrical readings and checking continuity in wires, among dozens of other functions.

Wow top post :17: Nice one!
 
unfortunately you will have to drain a little bit at a time. Unsure how much water will be in sorry

Thanks yet again for your help.
According to reply from " Croppie ", I will need more than a bucket !!
Anyway thanks for your time.
Kindest
 
Thanks yet again for your help.
According to reply from " Croppie ", I will need more than a bucket !!
Anyway thanks for your time.
Kindest

Hope you get it sorted, follows Croppies advice and you won't go far wrong :sunny:
 
Thanks for your reply. Somebody else tried to explain it once before, but it seemed so complicated. Your explanation hopefully will not screw my brain too much.
Seems as though others liked it as well.
Why do you think it may be a balancing problem as opposed to sludge??
Thanks anyway
 
Thanks for your reply. Somebody else tried to explain it once before, but it seemed so complicated. Your explanation hopefully will not screw my brain too much.
Seems as though others liked it as well.
Why do you think it may be a balancing problem as opposed to sludge??
Thanks anyway

Plumbers nose ;-)
 
Sorry Ex-pat, just re-checked the post. Remark not directed at you. Someone asked about funny name of boiler and queried where you were. Should have picked up the quote as I can't find it now. Humble pie eaten.
 
Although rereading that it looks more like a balancing issue!

How To Balance Radiators
Tool List:

Radiator-bleeding key
Lockshield valve adjuster or adjustable spanner
Screwdriver
Digital thermometer or multimeter with thermometer function



1. Make sure all the radiators have been bled. Turn off the central heating and allow the radiators to cool.

2. Familiarise yourself with the valves. The lockshield will usually have a push-on cap or one that is secured with a screw through the top. Remove it.

3. Older models will have a wheelhead valve on the other side — used to turn the radiator on/off.

4. Newer radiators will have a thermostatic valve instead of a wheelhead valve.

5. Open up the valves on all the radiators in the house by turning them anti-clockwise.Wheelhead and thermostatic valves can be turned easily by hand, but the lockshield will need a plastic adjuster to open it up. These come with new lockshield valves. A spanner will also do the job.

6. Turn the central heating back on and note down the order the radiators heat up. Those nearest the boiler normally get hot first. If you’ve got a lot of radiators, get assistance. Turn the heating off and wait while the radiators cool down.

7. When the radiators are cool, switch the heating back on and go to the first radiator on your list. Turn the lockshield valve clockwise until it is closed and then open it by a quarter of a turn. Once the radiator has warmed up, take a temperature reading at the pipework leading to one of the valves.

8. Now take a temperature reading at the pipework leading to the other valve and open the lockshield valve gradually until there’s a 12°C difference between now and the reading you took in step 7 (allow a couple of minutes after each adjustment for the temperature to change). The temperature figures indicated in the last step and this one are relevant to the radiator shown – don’t take them as any kind of optimum figure – it’s the 12°C difference in temperature at the valves that counts. Next, check the rest of the radiators in the system following the order in the list. The further you move away from the boiler, you’ll find the lockshield valve will have to be opened more. The last radiator may need to have the lockshield valve fully open to work at full efficiency. Your radiators are now balanced and should work perfectly.

Getting A Temperature

A key part of this job is measuring the temperature difference across each radiator. Specially designed thermometers that strap round the pipes at either end of the radiator are available to buy or hire, but it’s not really necessary to use these. You can get away with a single digital thermometer — it just means that you can’t take simultaneous readings and you’ll have to move from one end of the radiator to the other.

Digital thermometers are available from around £10. Alternatively, some digital multimeters have a temperature sensor function. A digital multimeter with temperature function costs from £25 and can also be used for taking electrical readings and checking continuity in wires, among dozens of other functions.

Excellent post Croppie. Are you commercial?
 
Before taking the time to do a complete balance. Close down all other radiators.

If the problem radiator then gets hot you can discount sludge or a sticking valve.

It may even push any minor blockages clear?
 
Status
Not open for further replies.

Similar plumbing topics

I have a home with an oil boiler in a garage...
Replies
0
Views
637
Replies
0
Views
449
What he said. Looks like 15mm copper conns...
Replies
7
Views
2K
L
Replies
2
Views
2K
B
Context for issue: I'd like to start by...
Replies
0
Views
561
Butchy10
B
Back
Top