Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Hob working pressure in the Gaining Plumbing Experience area at Plumbers Forums

Thoggy

Plumbers Arms member
Plumber
Gas Engineer
Messages
326
Hi all doing a landlords cert on hob in place, it's a shop put all 5 burners on and getting 24mb at meter not got the adapter to check on hob it's self I no it's 21 plus minus 2 so should I get Transco out,it goes off the meter in 22mm then into 28mm strangely for about 6 meters then back to. 22mm for a meter then ends with 2 meter of 15mm. Any advice appreciated dont do that much with hobs and don't want to shut the shop from cooking if I'm bring over the top. Cheers Martyn.
 
I guess, whoever it was run out of 22 on the day and had to put 28 in to keep the shop going. Looks like the governor is out. Make sure your ticket covers the set up. Yes, Martyn, it is for the gas transporter to sort it out.
 
Last edited:
Hi all doing a landlords cert on hob in place, it's a shop put all 5 burners on and getting 24mb at meter not got the adapter to check on hob it's self I no it's 21 plus minus 2 so should I get Transco out,it goes off the meter in 22mm then into 28mm strangely for about 6 meters then back to. 22mm for a meter then ends with 2 meter of 15mm. Any advice appreciated dont do that much with hobs and don't want to shut the shop from cooking if I'm bring over the top. Cheers Martyn.
1mbar,working pressure at meter a little over but not a concern if gas rate on hob worked out ok, you did gas rate hob when unable to test working pressure at hob.?
 
The smaller tube to fit onto hob to get working pressure at the appliance. Gas rated at 13.4kw with 5 burners on
 

Similar plumbing topics

Thank you for the replies. I had another...
Replies
4
Views
836
Absolute cock & bull from SGN, think about...
Replies
8
Views
2K
LPG lock up pressure can be regarded as the...
Replies
4
Views
1K
J
Replies
3
Views
2K
Was re-checked and passed no ID. pressure 15.5mbar
2 3
Replies
57
Views
14K
Back
Top