Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Hot water ok, no central heating in the Central Heating Forum area at Plumbers Forums

Status
Not open for further replies.
F

freddier

I have a ACL Drayton LP722, the hot water side is fine, however the central heating simply does nothing. I've bled everything I can find to bleed, several times, to no avail. I can get the rads nice & hot by manually switching the mid position valve with the hot water side on.

Any thoughts?
 
Thanks fuzzy, locked into the mid position but still no response from the boiler when the thermostat clicks.
 
arrhh, seems like a wiring fault then, if you are competent to do so you could link out the stat to see it it fires
 
check white cable on mid pos valve if 240v present when controls are calling but lever isnt moving valve is faulty probably get away with changing motor
 
Thanks Craig, would a faulty motor still account for the boiler not firing when the C/H stat "clicks"
 
yes when calling for heating the boiler will not fire untill valve has opened and microswitch in actuator has made
 
should have 240v at the white wire in wiring centre, if you have then check if you have 240v on the orange wire, if no then replace diverter. If yes the fault is back at the boiler
 
Thanks Craig, with that as the case it sums my promlem up to a tee.
Rory, Thanks. I'll check for voltage before I change the actuator motor.
 
Status
Not open for further replies.

Similar plumbing topics

Sometimes the connection point of the cylinder...
Replies
3
Views
559
it is brand new ( 6 months old ) Worcester gas...
Replies
2
Views
682
losing pressure
L
Can central heating / gas engineer expert help...
Replies
0
Views
824
L
Replies
2
Views
2K
Back
Top